First of all would like to say thanks to anyone who can answer my question.
Question is I have an arc welder that is 115 volt and says it operates at 26.6 amps.
I was told before and pretty sure even the box of 12-2g wire says that u should only use a 20 amp breaker on 12-2g
If i were to run a circuit for it what should i make it, 30 amp breaker and 10-2g ? I shouldnt even try it on a 20 amp breaker 12-2g circuit should i.
Thanks.
Question is I have an arc welder that is 115 volt and says it operates at 26.6 amps.
I was told before and pretty sure even the box of 12-2g wire says that u should only use a 20 amp breaker on 12-2g
If i were to run a circuit for it what should i make it, 30 amp breaker and 10-2g ? I shouldnt even try it on a 20 amp breaker 12-2g circuit should i.
Thanks.

#3
Member
Thread Starter
Join Date: Feb 2009
Location: Indiana
Posts: 21
Received 0 Votes
on
0 Posts
Says duty cycle 100 % up to 50 amps
Tapers to 20 % at 100 amps
The plug on the end looks to be replaced(its says 15 120 on bottom). So i definatly need to replace the plug to a 20 amp one.The wire on the plug doesn't look like very heavy ( if i had to guess id say 12gauge plug wire) and i was think of replacing it too. i might take it apart and see if it looks like its original or replaced and change it to heavier.
Tapers to 20 % at 100 amps
The plug on the end looks to be replaced(its says 15 120 on bottom). So i definatly need to replace the plug to a 20 amp one.The wire on the plug doesn't look like very heavy ( if i had to guess id say 12gauge plug wire) and i was think of replacing it too. i might take it apart and see if it looks like its original or replaced and change it to heavier.
#4
Then I would say 30 amp circuit.
You'll need to get an RV plug/receptacle or an L5-30P & R if you want twist-lock.
I wouldn't change the cord, depending on the insulation, not the wire size, it may be already good for 30 amps.
You'll need to get an RV plug/receptacle or an L5-30P & R if you want twist-lock.
I wouldn't change the cord, depending on the insulation, not the wire size, it may be already good for 30 amps.
#5
Member
Thread Starter
Join Date: Feb 2009
Location: Indiana
Posts: 21
Received 0 Votes
on
0 Posts
Thanks, Will be so nice when i can weld 2 pieces of metal together
30 amp is definalty new to me and prolly explains why the plug looks replaced.