Sharing conduit
#1
Member
Thread Starter
Join Date: Jan 2009
Location: Texas
Posts: 8
Received 0 Votes
on
0 Posts
Sharing conduit
I have two subs in which one of them will be fed with 4awg Thhn conductors and the other with 6/3 romex. Would sharing these feeds in the same conduit abide by code? Do i even need conduit for indoor runs? Planning on using flexible conduit if indeed required. Thanks!
#2
No, not normally would you need conduit for indoor runs. Unless it's required by your local codes.
Just to be safe, you may want to check with your local authority.
To get all that in a conduit, you'd probably need a 2".
You'll need to derate the 6/3 to the 60deg chart. For the #4's in conduit, you can use the 75 deg chart.
Just to be safe, you may want to check with your local authority.
To get all that in a conduit, you'd probably need a 2".

You'll need to derate the 6/3 to the 60deg chart. For the #4's in conduit, you can use the 75 deg chart.
#4
Member
Thread Starter
Join Date: Jan 2009
Location: Texas
Posts: 8
Received 0 Votes
on
0 Posts
I appreciate the replies everyone.
My conduit will be running through Sheetrock.........what fittings would i need to create a water tight seal between conduit and Sheetrock??
In addition, i have a 125amp service, is there (i have balancing in consideration) an NEC code that restricts a sub's amperage as a ratio of the service?
My conduit will be running through Sheetrock.........what fittings would i need to create a water tight seal between conduit and Sheetrock??
In addition, i have a 125amp service, is there (i have balancing in consideration) an NEC code that restricts a sub's amperage as a ratio of the service?
#5
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,807
Received 0 Votes
on
0 Posts
The common conduits we used are EMT , IMC , Ridge , PVC { electrical conduit not the plumming conduit please }
If you use the EMT you can use the setscrew with proper juction box however you can get them in compression fitting a major gotcha if you going to use in wet location it must be listed as raintight. { the package will tell ya on that part }
For PVC you will need a termail adpator with pvc glue to glue it together.
In addition, i have a 125amp service, is there (i have balancing in consideration) an NEC code that restricts a sub's amperage as a ratio of the service?
Keep in your mind with all the subpanel you need to bring in 4 conductors { black , red , white et green } and at the subpanel keep the netural and grounding conductors seperated.
If your subpanel do not have grounding bar you will have to get it many big box store will have this on hand and they are only few euros { bucks }
Merci,Marc
#6
this is either deja vu or I repsonded to this person on another forum.
hasn't the current codes outlawed NM in conduit except for short protective nipples?
and waterproof between sheetrock and conduit?
Sheetrock absorbs water. You had better stop the water long before it gets to the sheetrock.
you need to caulk the hole in the outer wall around the conduit.
hasn't the current codes outlawed NM in conduit except for short protective nipples?
and waterproof between sheetrock and conduit?
Sheetrock absorbs water. You had better stop the water long before it gets to the sheetrock.
you need to caulk the hole in the outer wall around the conduit.
#7
Member
Thread Starter
Join Date: Jan 2009
Location: Texas
Posts: 8
Received 0 Votes
on
0 Posts
Yes, the sum of the subs max amp usage is less than the service of 125. So your implication is that as long as the subs are less, then any feed size is allowed?? You have the code for that? Merci Merci