20a GFCI???

Two questions...

1) I have seen a few GFCI outlets at the store that say they're rated for 20a, but they do not have the t-shaped neutral slot. What is the purpose of this?

2) I have some left over 20a GFCI outlets that do have the t-shaped slot. Can I use these on a 15a/14ga circuit? I'm guessing the answer is NO!!!, but this is in my own house and I know I will never plug a 20a device in to them.

Thanks,
Rich
 
Sponsored Links
  #2  
Old 03-06-09, 11:08 AM
Member
Join Date: Oct 2005
Location: Milwaukee WI
Posts: 1,338
Received 0 Votes on 0 Posts
Originally Posted by bajafx4 View Post
Two questions...

1) I have seen a few GFCI outlets at the store that say they're rated for 20a, but they do not have the t-shaped neutral slot. What is the purpose of this?

2) I have some left over 20a GFCI outlets that do have the t-shaped slot. Can I use these on a 15a/14ga circuit? I'm guessing the answer is NO!!!, but this is in my own house and I know I will never plug a 20a device in to them.

Thanks,
Rich
1) Generally all duplex GFCIs are rated 20A feed-thru, which means you can use one as the first device on a circuit requiring GFCI protection. Although each recep is rated for 15A, you can connect a T-blade recep to the 20A feed-thru.

2. You are correct. "Can I use" is ambiguous. You may mean "Does code permit use of". All codes assume that you will either die or sell the place without any documentation of stuff you would never do.
 
  #3  
Old 03-06-09, 11:40 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Originally Posted by bajafx4 View Post
I have seen a few GFCI outlets at the store that say they're rated for 20a, but they do not have the t-shaped neutral slot. What is the purpose of this?
They are rated for 20A feed-through which means they can provide downstream protection for a 20A circuit. These are also duplex receptacles means you could pull 10A on each outlet of the receptacle for a total of 20A, but not exceeding 15A on either.

I have some left over 20a GFCI outlets that do have the t-shaped slot. Can I use these on a 15a/14ga circuit?
No, that violates code. You can use 15A recepts on a 20A circuit, but not 20A recepts on a 15A circuit.
 
  #4  
Old 03-06-09, 12:08 PM
Member
Thread Starter
Join Date: Feb 2009
Location: Grosse Ile, Michigan
Posts: 123
Received 0 Votes on 0 Posts
Ok, I figured I couldn't... or shouldn't use the 20a GFCI's on the 15a circuit. No problem there, I'll just get some new ones.

I'm still a little confused about the 20a GFCI outlets without the t-shaped neutral though. Do I understand that these can can provide 20a to downstream protected outlets, but the outlets on the actual GFCI are only good for 15a? If that's the case, why would you ever buy or install one of these instead of a true 20a GFCI w/ a t-shaped neutral?
 
  #5  
Old 03-06-09, 12:15 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Originally Posted by bajafx4 View Post
Ok, I figured I couldn't... or shouldn't use the 20a GFCI's on the 15a circuit. No problem there, I'll just get some new ones.
You can't use the t-slot 20A recepts on a 15A circuit, but you can use 20A feed-through recepts on a 15A circuit as long as the recept does not have the t-slot.

I'm still a little confused about the 20a GFCI outlets without the t-shaped neutral though. Do I understand that these can can provide 20a to downstream protected outlets, but the outlets on the actual GFCI are only good for 15a?
Correct.

If that's the case, why would you ever buy or install one of these instead of a true 20a GFCI w/ a t-shaped neutral?
The true 20A recepts are about $1.00 more expensive. Believe it or not some people are also incredibly picky about unimportant things and will complain about the t-slot looking different than the other recepts.
 
  #6  
Old 03-06-09, 12:30 PM
Member
Thread Starter
Join Date: Feb 2009
Location: Grosse Ile, Michigan
Posts: 123
Received 0 Votes on 0 Posts
Originally Posted by ibpooks
You can't use the t-slot 20A recepts on a 15A circuit, but you can use 20A feed-through recepts on a 15A circuit as long as the recept does not have the t-slot.
I will just buy the 15a GFCI outlets. I don't see any advantage to have the ability to pass through 20a when this circuit is on a on a 15a breaker w/ 14ga wire. Correct?

Originally Posted by ibpooks
The true 20A recepts are about $1.00 more expensive. Believe it or not some people are also incredibly picky about unimportant things and will complain about the t-slot looking different than the other recepts.
Hah... I thought the t-slot was a status symbol!
 
  #7  
Old 03-07-09, 07:13 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,996
Received 39 Votes on 34 Posts
Originally Posted by bajafx4 View Post
I will just buy the 15a GFCI outlets. I don't see any advantage to have the ability to pass through 20a when this circuit is on a on a 15a breaker w/ 14ga wire. Correct?
That would be correct. As long as there is more than 1 place to plug into the 15 amp receptacles can be used on a 20 amp circuit with #12 wire. This is why the ability to pass through is important.
 
  #8  
Old 03-07-09, 07:48 PM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
I'm not even sure they make GFCIs without a 20-amp pass-through. I think they all have this. In fact, I would venture to guess that all outlets of any kind (GFCI or not) sold today have at least 20 amp pass through.
 
  #9  
Old 03-07-09, 08:29 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,996
Received 39 Votes on 34 Posts
I believe you are correct John.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: