Wiring 5000W garage heater

Reply

  #1  
Old 03-09-09, 03:45 PM
S
Member
Thread Starter
Join Date: Nov 2004
Location: north dakota
Posts: 175
Received 0 Votes on 0 Posts
Wiring 5000W garage heater

I have a chance to replace a 4Kw heater (broken) with a 5Kw heater.
The 4K had been hardwired (conduit) from the panel to the heater with 10/3 and a 30A breaker.
Can the 5Kw heater use the same wire & breaker?

Or, basically, what wire size & breaker for a 5000W heater?
SteveS
 
  #2  
Old 03-09-09, 03:53 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
What voltage?



,,,,,,,,,,,,,,,,,,,,,
 
  #3  
Old 03-09-09, 07:26 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,915
Received 283 Votes on 247 Posts
At 240 volts your just a hair under 21 amps so you will be fine with your existing circuit.
 
  #4  
Old 03-09-09, 08:07 PM
S
Member
Thread Starter
Join Date: Nov 2004
Location: north dakota
Posts: 175
Received 0 Votes on 0 Posts
Yes, 240V. Knew I'd leave something out. (Although I haven't seen too many 5000W-120V heaters lately)

I've been given conflicting info relating to breaker size & wire size. I understood 10/3 & 30A would be OK. Majority rules.
Thanks Ironhand.
 
  #5  
Old 03-09-09, 09:39 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,942
Received 44 Votes on 42 Posts
Yes, your #10 and 30A breaker is good for a 240V heater up to 5760W.

(Although I haven't seen too many 5000W-120V heaters lately)
Sometimes people buy used commercial heaters which are designed for 208V, 277V, etc.
 
  #6  
Old 03-09-09, 10:22 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
Not 10-3, 10-2. No neutral needed on a 240v appliance.
 
 