ok I have got 250' of #2 quad plex /polomino wire to go from my house to pole to pole next to my barn then to weather head on barn . to get inside each place, outside house into my 200 amp panel and from barn gable end to its new panel i was going to use ser 2-2-2-4 . ok total run from building to building is 200 ' . so my question is to use a 100 amp breaker comming out of my 200 panel should it be single or double pole and why ???
thanks

#2
If you install a single pole breaker you will only be able to supply 120 volt loads from the panel. A double pole breaker will allow you to run either 120 or 240 volt loads from the panel.
If you installed a single pole breaker only every other buss finger would be hot in your panel.
If you installed a single pole breaker only every other buss finger would be hot in your panel.
#3
Double pole, because that supplies 240V. Also because no one manufactures a single pole 100A breaker.