Shop subpanel feeder for rgray422

hey guy...im new to this site and found your response to a similar predicament and thought you may be able to help me. ive been a professional cabinetmaker for almost 30 yrs and just now building my own small shop at home, approx. 500 sq ft. i plan on wiring a sub panel to my shop from my main panel which has plenty of room for it. im not an electrician but during my years of construction i have picked up some knowledge. an electrical contractor on a previous job gave me this advice when i told him what i was planning. he suggested a 6/3 and #10 ground to the shop....im planning on a 220 line for a table saw in the future.....a 100 amp breaker at the incoming panel and a 30 amp for the 220 and two 20 amps for lighting and outlets at the subpanel. what do you think?
 
Sponsored Links
  #2  
Old 03-21-09, 11:05 PM
Forum Topic Moderator
Thread Starter
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
rgray--

If you want to use 6/3 cable for the shop subpanel, you'll need to use type UF-B waterproof "underground feeder" cable instead of the usual NM-B "non-metallic romex" which is not waterproof. This type of cable can power a 60A subpanel at a distance of up to about 150'. If the distance from the house to the shop is longer than that, you'll need to select a larger cable.

A 60A panel should be sufficient for shop lighting and wood working tools. If you plan to use metal working tools like a welder or plasma cutter, then a 100A subpanel with appropriate sized cable may be required.

You will need to install a ground rod at the shop, bonded to the subpanel ground bar using #6 copper wire and an acorn clamp. The subpanel needs to have isolated ground and neutral bars; this usually requires you to purchase an add-on ground bar kit for the panel and to remove the factory-installed bonding screw or strap.

Instead of installing any cable or breakers for your future table saw, I recommend that you install a 1/2 or 3/4 conduit from the shop subpanel to the expected table saw location. You can then install the correct size wire and breaker when you select the table saw.

A 500 sq. ft. shop will likely require more than two 20A circuits. I would start with one 20A for lighting and then run a dedicated 20A circuit to each tool location, and a general-purpose 20A circuit to each "workbench" location. You also may want to consider a 20A circuit on a cord-reel hung from the ceiling. All 120V receptacles must have GFCI protection. Don't forget the exterior lighting which is required at all grade-level entrances.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: