220V GFCI breaker
#1
Member
Thread Starter
Join Date: Jan 2008
Location: Mountain View, CA
Posts: 69
Received 0 Votes
on
0 Posts
220V GFCI breaker
As you are probably aware already
I am putting a hottub in my back yard. Most of the "cutoff" boxes seem to come with GFCI built in, so the simple thing would seem to be to use a regular breaker at the panel and the GFCI at the cutoff. I've not done a GFCI 220V breaker before, so the question is, does it need the neutral? The hot tub is 3-wire (no neutral needed for it) and the outlet required by code won't be on the same circuit, so I'm thinking I'll save a little $ by not pulling a neutral.
Also, I was planning to use 1" conduit, but with only 3 wires, maybe 3/4" would be fine? (50amp breaker, 120' of run, total)
Thanks!

Also, I was planning to use 1" conduit, but with only 3 wires, maybe 3/4" would be fine? (50amp breaker, 120' of run, total)
Thanks!
#4
Most hot tubs require two hots and a neutral. You may want to double check the specs. Since you are running PVC pipe you will also need a ground.
I would also suggest the Cutler Hammer tub disconnect. It has the GFCI breaker plus 2 extra slots for a receptacle.
I suggest sticking with the 1" PVC can be tough to pull through sometimes.
I would also suggest the Cutler Hammer tub disconnect. It has the GFCI breaker plus 2 extra slots for a receptacle.
I suggest sticking with the 1" PVC can be tough to pull through sometimes.
#5
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,807
Received 0 Votes
on
0 Posts
Yeah there is 220 volt GFCI breaker on market.
Most hottubs in the states are useally have two hot conductors and netural very few hot tubs do have straight 240 volt set up.
Keep in your mind with disconnection switch the codes will require them withen 5 feet IIRC.
Most hot tub installment I useally dealt with it most case it will be wise to run with 1 inch PVC conduit it make it little more easier to pull it thru the conduit and also make sure the ground conductor is green the bare conductor in this area is not allowed
Note: the only time it will be allowed the bare conductor is indoor but when you get to the outdoor side you must change it by putting in junction box and run green conductor from there.
Merci,Marc
Most hottubs in the states are useally have two hot conductors and netural very few hot tubs do have straight 240 volt set up.
Keep in your mind with disconnection switch the codes will require them withen 5 feet IIRC.
Most hot tub installment I useally dealt with it most case it will be wise to run with 1 inch PVC conduit it make it little more easier to pull it thru the conduit and also make sure the ground conductor is green the bare conductor in this area is not allowed
Note: the only time it will be allowed the bare conductor is indoor but when you get to the outdoor side you must change it by putting in junction box and run green conductor from there.
Merci,Marc
#6
Member
Join Date: Feb 2009
Location: Iowa
Posts: 339
Received 0 Votes
on
0 Posts
It also sound like you will have it somewhere in your yard. Where will this hot tub be sitting on? Grass?, Concrete?, Wood?
Jim
Jim

Last edited by pcboss; 05-04-09 at 06:29 AM. Reason: removed ground rod comment
#7
Member
Thread Starter
Join Date: Jan 2008
Location: Mountain View, CA
Posts: 69
Received 0 Votes
on
0 Posts
Why do you say the disconnect will need a ground rod? It's not a subpanel in a seperate structure, and I didn't see it in section 680, and it hasn't come up on any of the descriptions of installations that I've seen, even when the disconnect is away from the house, so I'll need more to go on.
I see that even though the hot tub doesn't need neutral, the GFCI will. It looks like a GFCI breaker in the panel and a cheap (non-GFCI) disconnect box would let me save $ by not using 100' of 6# for neutral.
Thanks for the help!
Last edited by pcboss; 05-04-09 at 06:35 AM. Reason: removed ground rod comment
#8
The disconnect will NOT require a grounding rod.
If you install the GFI breaker at the main house panel you will connect the neutral pigtail to the buss. You would not need to run a neutral to the tub if the specs do not call for one.
You would still need the green insulated grounding conductor.
If you install the GFI breaker at the main house panel you will connect the neutral pigtail to the buss. You would not need to run a neutral to the tub if the specs do not call for one.
You would still need the green insulated grounding conductor.
#9
Member
Join Date: Feb 2009
Location: Iowa
Posts: 339
Received 0 Votes
on
0 Posts
The specs seem pretty clear that a separate neutral is not needed. They are at http://www.jacuzzihottubs.com/reques...7_J400_LCD.pdf
It will be on EZ Pad (plastic) over compacted sand and soil. No metal nearby to require bonding.
Why do you say the disconnect will need a ground rod? It's not a subpanel in a seperate structure, and I didn't see it in section 680, and it hasn't come up on any of the descriptions of installations that I've seen, even when the disconnect is away from the house, so I'll need more to go on.
I see that even though the hot tub doesn't need neutral, the GFCI will. It looks like a GFCI breaker in the panel and a cheap (non-GFCI) disconnect box would let me save $ by not using 100' of 6# for neutral.
Thanks for the help!
It will be on EZ Pad (plastic) over compacted sand and soil. No metal nearby to require bonding.
Why do you say the disconnect will need a ground rod? It's not a subpanel in a seperate structure, and I didn't see it in section 680, and it hasn't come up on any of the descriptions of installations that I've seen, even when the disconnect is away from the house, so I'll need more to go on.
I see that even though the hot tub doesn't need neutral, the GFCI will. It looks like a GFCI breaker in the panel and a cheap (non-GFCI) disconnect box would let me save $ by not using 100' of 6# for neutral.
Thanks for the help!
Jim

#10
I've not done a GFCI 220V breaker before, so the question is, does it need the neutral?
I'm thinking I'll save a little $ by not pulling a neutral.
Also, I was planning to use 1" conduit, but with only 3 wires, maybe 3/4" would be fine? (50amp breaker, 120' of run, total)