Wire Size

Bought some 14 AWG Romex a while back. While wiring I got the feeling that the wires were not as thick as I was used to. When I compared to some 14 AWG Romex I still had in the garage, I could tell just by looking at it that the newer Romex conductors were thinner than the older ones. Are the smaller conductors still approved, and why does it say 14 AWG when they are definitely smaller?
 
Sponsored Links
  #2  
Old 05-09-09, 07:32 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
You have to look at the conductor not the insulation. Newer insulation is better therefore doesn't have to be as thick.
 
  #3  
Old 05-09-09, 08:11 PM
Member
Thread Starter
Join Date: Nov 2002
Location: San Francisco Peninsula
Posts: 121
Received 0 Votes on 0 Posts
I certainly looked at the conductors, not the insulation, which does not carry any current.
 
  #4  
Old 05-09-09, 08:13 PM
Member
Join Date: Apr 2009
Location: Boston
Posts: 146
Received 0 Votes on 0 Posts
perhaps what you originally had was 12. 14 gauge is 14 gauge
 
  #5  
Old 05-09-09, 09:16 PM
Member
Join Date: Jul 2008
Location: Kingston, PA
Posts: 137
Received 0 Votes on 0 Posts
I do remember reading a thread on another forum wherein it was discussed older 14awg wire was in fact thicker than today. I think it had to do with the metal alloy that used to be used. I will try to find it...
 
  #6  
Old 05-09-09, 10:51 PM
Member
Thread Starter
Join Date: Nov 2002
Location: San Francisco Peninsula
Posts: 121
Received 0 Votes on 0 Posts
What I originally had was 14 AWG, which is what is clearly stamped on the Romex jacket; a 12 AWG is much thicker and is stamped with 12 AWG, not 14 AWG.
 
  #7  
Old 05-10-09, 08:08 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,999
Received 40 Votes on 35 Posts
The American wire gauge standard has not changed. A #14 wire from the past is the same size as a #14 from today.
 
  #8  
Old 05-10-09, 08:36 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
  #9  
Old 05-10-09, 09:02 AM
Member
Join Date: Jan 2008
Location: Mountain View, CA
Posts: 69
Received 0 Votes on 0 Posts
One possibility (and I'm just speculating) is that "14 AWG" is a *minimum* size, and a manufacturer in the past may have found that making it a little oversize made up for looser manufacturing tolerances, meaning fewer failed quality checks and associated issues. But then, with the price of copper heading up and high-spec manufacturing equipment becoming more common, more recent economics may have meant that investing in better equipment to tighten the tolerances was worth the investment. If this is right, then your new wire should be 14 AWB and the old wire should be a bit bigger.
 
  #10  
Old 05-10-09, 09:51 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
I vote for RichA's explanation.
 
  #11  
Old 05-10-09, 10:25 AM
Member
Join Date: Apr 2009
Location: Boston
Posts: 146
Received 0 Votes on 0 Posts
Originally Posted by hukre View Post
What I originally had was 14 AWG, which is what is clearly stamped on the Romex jacket; a 12 AWG is much thicker and is stamped with 12 AWG, not 14 AWG.
The actual cross sectional area that AWG #14 has not changed. According to you the wire in one was thicker, did you measure this? How can you be sure? What tools did you use to accurately measure the cross sectional area of the wire to determine the differences in wire gauge?
 
  #12  
Old 05-12-09, 10:51 PM
Member
Thread Starter
Join Date: Nov 2002
Location: San Francisco Peninsula
Posts: 121
Received 0 Votes on 0 Posts
Thanks to all who took the time to send in a reply. I will look into measuring the different conductors with a precision micrometer (unfortunately I don't have one myself) and let you know the results.
 
  #13  
Old 05-13-09, 09:35 AM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,456
Received 15 Votes on 15 Posts
Some months ago, I measure with dial calipers my 53 year old romex in the house to brand new southwire. The copper was within .001", the insulation today was close to 1/2 the thickness of the old. These days, the trend is to use a nylon thin jacket over PVC, I believe to increase the cut-thru resistance.
 
  #14  
Old 05-13-09, 09:52 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Solid #14 wire diameter should be at least 0.0641 inches (1.628 mm). I don't know what the acceptable manufacturing tolerances are to still meet code, but my guess is that one of your pieces is on the low side of tolerance and one is on the high side.
 
  #15  
Old 05-13-09, 04:07 PM
Member
Thread Starter
Join Date: Nov 2002
Location: San Francisco Peninsula
Posts: 121
Received 0 Votes on 0 Posts
Was able to have the conductors measured. All three are about .053" diameter, which is closer to a 16 AWG than a 14 AWG. I just hope they don't overheat.
The following is what is printed on the Romex jacket (just in case someone may think I measured some other type of wire): "ESSEXEP.COM 14-2G NON-METALLIC SHEATHED CABLE TYPE NM-B 600V E10816A (UL) 12 JAN 2005 00:54 E1"
 
  #16  
Old 05-13-09, 04:18 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Made in China? I have had a lot of trouble with smaller than spec things from China such as galvanized pipe fittings that wouldn't hold water and alleged 8-32 machine screws that just pulled out of a standard 8-32 threaded hole. Once went to install a Chinese made door bell transformer with a " conduit nipple and after threading on the conduit nut it just fell off the nipple was so under sized.
 
  #17  
Old 05-13-09, 06:26 PM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,456
Received 15 Votes on 15 Posts
That wire is dangerous..

Hukre; I would say several agencies would be interested in this finding. Namely, US customs, UL, and Product Safety.
 
  #18  
Old 05-14-09, 12:28 PM
Member
Join Date: Mar 2004
Location: New Jersey, USA
Posts: 56
Received 0 Votes on 0 Posts
If this is solid, not stranded, wire then you don't need to buy a micrometer to see if there is a difference in thickness.

Lay two short, stripped, straight lengths of wires next to each other, say 2 or 3 inches apart. Place a ruler on top of the wires, holding it so the straight-edge touches against the wires. Is one end of the ruler noticeably higher off the table then the other? If yes, the wire diameters are significantly different.
 
  #19  
Old 05-28-09, 11:41 AM
Member
Join Date: May 2009
Posts: 2
Received 0 Votes on 0 Posts
Originally Posted by ray2047 View Post
I second these wires. I purchased the same ones a few weeks ago and they work great!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: