Ground wire size...

I have a question for the ground to the load center.

Lets just say, hypothetically, you are using #6 wiring to a subpanel, should the ground wire also be #6?
 
  #2  
Old 05-12-09, 07:56 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,941
Received 45 Votes on 43 Posts
The equipment grounding conductor would usually be #10 copper to match #6 copper hots. A #8 ground could be justified in some circumstances.
 
  #3  
Old 05-12-09, 08:10 AM
Z
Member
Thread Starter
Join Date: Oct 2008
Location: NYC
Posts: 433
Received 0 Votes on 0 Posts
The #6 was a hypothetical..is there a calculation for ground wire size? What if it was a 2/0 feed?
 
  #4  
Old 05-12-09, 08:25 AM
P
Member
Join Date: Feb 2002
Location: port chester n y
Posts: 2,117
Received 0 Votes on 0 Posts
What determined the size of an Equiptment Grounding Conductor is the rating of the circuit-breaker that protects the conductors. Table 250.122 is referred to when determining the size of the EGC.
 
  #5  
Old 05-12-09, 08:28 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,941
Received 45 Votes on 43 Posts
NEC Table 250.122 lists the required minimum equipment ground conductor size for the given maximum overcurrent protection device. The actual size of the ground may have to be adjusted up however based on both the breaker size protecting the hots and the size of the hots themselves, so without knowing how exactly your hypothetical #6 or #2/0 was used, I can't give an exact answer for the ground size.

In the most typical case, #2/0 copper hots would warrant a #6 copper ground.
 
  #6  
Old 05-12-09, 08:38 AM
Z
Member
Thread Starter
Join Date: Oct 2008
Location: NYC
Posts: 433
Received 0 Votes on 0 Posts
I am not looking for an exact answer or an exact wire size, this was something I was thinking about when I replaced a disconnect switch last week in my garage. I was simply curious.

Thanks for the comments.
 
 