Conduit sharing 120 vac & 240 vac

From the main panel, I want to drop a 120 vac circuit from its own breaker, and a 240 vac circuit from its own breaker... then run them both in a common conduit (30 - 40 feet) to a box, where the 120v will branch off to its final use... the 240v wiring will continue on to a sub-panel. Is it OK to run these two sets of wires together in the initial length of conduit?
 
  #2  
Old 05-20-09, 07:11 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,942
Received 44 Votes on 42 Posts
Provided that 40% conduit fill is not exceeded, derating is calculated, and neither circuit is used to power a pool, spa or similar installation; your plan is acceptable.
 
  #3  
Old 05-20-09, 07:26 PM
K
Member
Thread Starter
Join Date: May 2009
Location: Florida Panhandle
Posts: 2
Received 0 Votes on 0 Posts
Thank you. I'll calc. the conduit & wire size/fill
 
  #4  
Old 05-20-09, 07:56 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,247
Received 111 Votes on 97 Posts
Please make sure you run a 4 wire feed to the subpanel. Two hots, 1 neutral and a grounding conductor.
 
 