Conduit sharing 120 vac & 240 vac
#1
Member
Thread Starter
Join Date: May 2009
Location: Florida Panhandle
Posts: 2
Received 0 Votes
on
0 Posts
Conduit sharing 120 vac & 240 vac
From the main panel, I want to drop a 120 vac circuit from its own breaker, and a 240 vac circuit from its own breaker... then run them both in a common conduit (30 - 40 feet) to a box, where the 120v will branch off to its final use... the 240v wiring will continue on to a sub-panel. Is it OK to run these two sets of wires together in the initial length of conduit?
#2
Provided that 40% conduit fill is not exceeded, derating is calculated, and neither circuit is used to power a pool, spa or similar installation; your plan is acceptable.