Proper wire for outdoor use in Conduit


  #1  
Old 06-02-09, 09:48 PM
K
New Member
Thread Starter
Join Date: May 2009
Location: Hixon, TN
Posts: 35
Upvotes: 0
Received 0 Upvotes on 0 Posts
Proper wire for outdoor use in Conduit

I was at Lowes looking for THWN and they said all they had was THHN. But in looking at the wire they have it is marked with the following:
CU Type MTW THWN or THHN or Gasoline and Oil Resistant II or AWM 600 Volts VM-1

Will this work for use in outside Conduit?
 
  #2  
Old 06-02-09, 09:53 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 3,821
Upvotes: 0
Received 2 Upvotes on 2 Posts
most current thhn is dual rated as thhn/thwn and the thwn is what you need. What you saw is fine.
 
  #3  
Old 06-02-09, 10:14 PM
K
New Member
Thread Starter
Join Date: May 2009
Location: Hixon, TN
Posts: 35
Upvotes: 0
Received 0 Upvotes on 0 Posts
Great, it looked like it would work but I wanted to make sure. I got a 150' roll of green and one of white for half price along with a 100' roll of black.
 
  #4  
Old 06-03-09, 09:01 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Originally Posted by kreddick4
CU Type MTW THWN or THHN or Gasoline and Oil Resistant II or AWM 600 Volts VM-1

Will this work for use in outside Conduit?
Yes. The wire is multi-rated and meets several different standards MTW, THWN, THHN and AWM.
 
 