Proper wire for outdoor use in Conduit

I was at Lowes looking for THWN and they said all they had was THHN. But in looking at the wire they have it is marked with the following:
CU Type MTW THWN or THHN or Gasoline and Oil Resistant II or AWM 600 Volts VM-1

Will this work for use in outside Conduit?
 
Sponsored Links
  #2  
Old 06-02-09, 10:53 PM
nap's Avatar
nap
nap is offline
New Member
Join Date: May 2006
Location: north
Posts: 4,163
Received 1 Vote on 1 Post
most current thhn is dual rated as thhn/thwn and the thwn is what you need. What you saw is fine.
 
  #3  
Old 06-02-09, 11:14 PM
New Member
Thread Starter
Join Date: May 2009
Location: Hixon, TN
Posts: 44
Received 0 Votes on 0 Posts
Great, it looked like it would work but I wanted to make sure. I got a 150' roll of green and one of white for half price along with a 100' roll of black.
 
  #4  
Old 06-03-09, 10:01 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Originally Posted by kreddick4 View Post
CU Type MTW THWN or THHN or Gasoline and Oil Resistant II or AWM 600 Volts VM-1

Will this work for use in outside Conduit?
Yes. The wire is multi-rated and meets several different standards MTW, THWN, THHN and AWM.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: