Adding excessive breakers to box

I have a breaker box that has a 100amp main breaker. Also connected are a 20 amp breaker, and a 50 amp breaker for an RV hookup. I was planning on adding more outlets and thus more breakers. The problem is that I rarely use the 50 amp hookup, and typically leave it off. Is it possible to install a higher total of amps for the breakers than the main breaker and still be able to run it safely, assuming I keep the 50 amp turned off?

I.e., could I attach three more 20 amp breakers to the 100 amp box with one 20 amp and one 50 amp (a total of 130 amps), assuming the 50 amp breaker is turned off (presumably equaling 80 amps)?

Thank you.
 
Sponsored Links
  #2  
Old 06-16-09, 11:35 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,941
Received 30 Votes on 26 Posts
Adding the ratings of the breaker handles is not an accurate way of determining if the panel can serve the additional loads. If you were to look at a 200 amp panel the breaker handles might add up to 600-800 amps.

The correct way would be to do a demand load calculation.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: