can someone explain the "switchloop"?
I keep seeing this term, but don't understand the concept. can someone explain it? Or post a diagram of the wiring layout?
Thanks.
Thanks.
#2
The wire going to the switch on the left is a switch loop because both wires hot; the white one is always hot, the black one is hot when the switch is ON. It can be thought of as a single loop of wire which is broken in the middle by the switch. The loop is only a partial circuit because the neutral wire remains in the light box.
Compare that to the receptacle on the right where only the black wire is hot and the white wire is neutral. This provides a complete circuit as it has both hot and neutral wires.
The practical implication is that if you hypothetically wanted to add another receptacle, you could extend a cable from the receptacle on the right, but you could not extend a cable from the switch because of the lack of neutral wire. Switch loops cannot be extended to do anything other than switch a load.
#3
Member
Thread Starter
Join Date: Jul 2005
Location: SF Bay Area
Posts: 850
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Excellent diagram. So in a switch loop setup, if I remove the switch and put a continuity tester to the wires, the tester shouldn't light?
trying to determine if I have power at my switch or a switch loop.
I put the tester on the wires and it lit up.
trying to determine if I have power at my switch or a switch loop.
I put the tester on the wires and it lit up.
#4
trying to determine if I have power at my switch or a switch loop.
I put the tester on the wires and it lit up.
I put the tester on the wires and it lit up.
#5
Member
Switch Loop
If you have only one cable coming into the switch box, you have a switch loop. Black wire on one screw and white wire on the other screw.
Two cables would indicate one is power in and the other sends current to the light. Black wire from the power cable on one screw and black wire going to light on the other screw. Two white wires connected together.
Two cables would indicate one is power in and the other sends current to the light. Black wire from the power cable on one screw and black wire going to light on the other screw. Two white wires connected together.
#6
Member
Thread Starter
Join Date: Jul 2005
Location: SF Bay Area
Posts: 850
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Appears I have a switch loop. Only one cable with only black, white, ground.
I have been attempting to add a exhaust fan/light combo. now I know why it hasn't worked the way it is laid out in the schematic.
I have been attempting to add a exhaust fan/light combo. now I know why it hasn't worked the way it is laid out in the schematic.
#7
Best way to tell you have a switch loop is what Wirepuller posted or if you have a white/white taped black connected to the switch and it is not a 3 way.
#8
Member
Thread Starter
Join Date: Jul 2005
Location: SF Bay Area
Posts: 850
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I don't know if this is an indicator, but the original switch I removed has three screws, one black, one brass/copper one side.
one copper screw on the other side.
knob & tube wiring.
one copper screw on the other side.
knob & tube wiring.
#9
Ooo Goody! A three way switch and knob and tube. You can not actually add anything to a K&T circuit. It is against code. Also a three-way on a K&T may be wired in a dangerous and non code acceptable way.
#11
It is the correct switch. It's the wiring that is suspect.The important thing is you can not add the fan to a K&T circuit. You need to run new wire from the breaker box.
I have been attempting to add a exhaust fan/light combo. now I know why it hasn't worked the way it is laid out in the schematic.
#12
Member
Thread Starter
Join Date: Jul 2005
Location: SF Bay Area
Posts: 850
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I plan to put the original switch back. It just had been bugging me that I couldn't figure out the wiring.
Electrician is coming for quote to do it correctly.
Electrician is coming for quote to do it correctly.
#13
Stumped1.,
It will be the best to get the electrician deal with this stuff espcally with T&K they are very tricky to deal with it and it don't take much to screw up and what more with three way formats there is about a dozen way to get the three way to work { 90% of them do not meet the modern codes and it was written way back in late 1930's }
I allready dealt with quite few of them in both North American and European verison.
And you can not extend the T&K circuit at all.
You must run the new one to slove the issue.
Merci,Marc
It will be the best to get the electrician deal with this stuff espcally with T&K they are very tricky to deal with it and it don't take much to screw up and what more with three way formats there is about a dozen way to get the three way to work { 90% of them do not meet the modern codes and it was written way back in late 1930's }
I allready dealt with quite few of them in both North American and European verison.
And you can not extend the T&K circuit at all.
You must run the new one to slove the issue.