Shed Help..

Looking for a little guidance guys. I am about to run electricity to my shed. I am gonna list what ill be running in the shed, not sure how to gauge the amps ill be running, could use some help with figuring that out.

1. will be a light mounted outside of building.
2. light mounted inside of building
3. 4 outlets inside (1 freezer, 1 bandsaw, 1 drill press)
4. 1 outlet outside of shed. (General purpose)

I currently have 6 guage/4 wire. Will this be sufficient?
I will be burying my cable 18 inches in sealed PVC conduit.
Plan on using a disconnect inside the shed.
At the moment everything I would be using is 120V, but would like to have 240V available.
How much amperage am i looking at?

How does this sound? Feel free to fill in any blanks I may be missing.
 
Sponsored Links
  #2  
Old 07-02-09, 10:39 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
What is 6 guage/4 wire? Are you installing a sub-panel? If so describe. Describe breaker at main panel you are going to feed it with.
 
  #3  
Old 07-03-09, 07:44 AM
D
Member
Thread Starter
Join Date: Jul 2009
Posts: 6
Received 0 Votes on 0 Posts
What is 6 guage/4 wire?
Sorry, I meant 6 awg /4 wire, type SOOW

Are you installing a sub-panel? If so describe.
I will be installing a sub panel, I havent purchased it yet. In my OP I stated i was looking for help guaging the amperage needed. I listed the loads I would be using. Based on the loads listed, what panel would be recommended?

Describe breaker at main panel you are going to feed it with.
I will be adding a new breaker to the main panel, once the amperage question is answered. I imagine it will be a 2 pole breaker to feed 240V. But this is still undecided.

Also wanted to add that it will be about 35 ft from the main breaker panel to the sub panel.
 

Last edited by drexendelsangre; 07-03-09 at 08:19 AM.
  #4  
Old 07-03-09, 08:34 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,174
Received 92 Votes on 79 Posts
Sorry, you will have to use another wiring method. Flexible cord like the SOOW is not to be used in place of permanent wiring.

Since you are talking about conduit you would just use individual conductors rated THHN/THWN to feed the subpanel in your shed. You would need 2 hots in black, 1 white neutral and 1 green ground.

With the #6 you could feed it with a 50 amp breaker and have plenty of power for your shed. You could also use #8 and a 40 amp breaker.

You will need to leave the neutrals and ground isolated from each other in the subpanel. You will also need a ground rod connected to the panel with a #6 copper conductor.
 
  #5  
Old 07-03-09, 08:43 AM
D
Member
Thread Starter
Join Date: Jul 2009
Posts: 6
Received 0 Votes on 0 Posts
does the amperage of the breaker change if i decide to go 240V? It would of course be a 2 pole breaker, but would a 50 amp 2 pole breaker work? or would that change the requirements?
 
  #6  
Old 07-03-09, 08:58 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,174
Received 92 Votes on 79 Posts
The breaker needs to be properly sized to protect the wire. Voltage will not matter.

A 2 pole breaker would just give you the ability to have 240 volt circuits and to lessen the load on a 120 volt feed to the shed because the load is split over the 2 hots legs instead of one.
 
  #7  
Old 07-03-09, 09:04 AM
D
Member
Thread Starter
Join Date: Jul 2009
Posts: 6
Received 0 Votes on 0 Posts
Thanks, gonna go get the cable you suggested now.
 
  #8  
Old 07-03-09, 09:08 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Originally Posted by drexendelsangre View Post
does the amperage of the breaker change if i decide to go 240V? It would of course be a 2 pole breaker, but would a 50 amp 2 pole breaker work? or would that change the requirements?
No the amperage of the supply breaker doesn't change but available power at the subpanel doubles. There would be no reason to do this 120v.

To anticipate your next question on size of subpanel I would suggest 100a so you have plenty of room for breakers. Yes, subpanel may be larger then the supply breaker. You will also need a main breaker in the subpanel if you have more then six breakers, Size of main breaker in subpanel should be equal to or greater then the main panel supply breaker.

I would suggest you buy a book such as Wiring Simplified available at Home Depot and study up on what you need to do.
 
  #9  
Old 07-03-09, 09:10 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Originally Posted by drexendelsangre View Post
Thanks, gonna go get the cable you suggested now.
He wasn't suggesting cable. He was suggesting individual wires.
 
  #10  
Old 07-03-09, 12:01 PM
D
Member
Thread Starter
Join Date: Jul 2009
Posts: 6
Received 0 Votes on 0 Posts
yeah, i gathered that much, thnx.
 
  #11  
Old 07-03-09, 08:52 PM
W
Member
Join Date: Mar 2008
Location: Cat Spring, Texas
Posts: 41
Received 0 Votes on 0 Posts
Originally Posted by drexendelsangre View Post
I am gonna list what ill be running in the shed,

1. will be a light mounted outside of building.
2. light mounted inside of building
3. 4 outlets inside (1 freezer, 1 bandsaw, 1 drill press)
4. 1 outlet outside of shed. (General purpose)

.
Assuming the shed will be closed up to prevent your bandsaw and drill press from walking off, be prepared for that freezer to add significantly to your electric bill. Enclosed fridges and freezers are the biggest "high bill complaint culprits" we have at our POCO.
 
  #12  
Old 07-04-09, 10:04 AM
D
Member
Thread Starter
Join Date: Jul 2009
Posts: 6
Received 0 Votes on 0 Posts
Originally Posted by WFOWFO View Post
Assuming the shed will be closed up to prevent your bandsaw and drill press from walking off, be prepared for that freezer to add significantly to your electric bill. Enclosed fridges and freezers are the biggest "high bill complaint culprits" we have at our POCO.
Im a locksmith by trade. The shed will plenty secure.
 
  #13  
Old 07-05-09, 08:07 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,407
Received 128 Votes on 119 Posts
Originally Posted by drexendelsangre View Post
Im a locksmith by trade. The shed will plenty secure.
I think what WFOWFO was stating didn't have anything to do with the security, but the fact that fridge and freezers in an enclosed space do not operate efficiently, due to both heat and lack of airflow. They need ventilation to work at their expected efficiencies. You should plan on some type of air movement to allow fresh air into the shed.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: