Pilot light on 2-pole switch not working

I have a Leviton 1222-PLG double-pole switch with a pilot light in the handle. The pilot light only works when there is no power to one "pole". Wondering if there's a workaround or if I'm doing something wrong.

On pole A is a 120V circuit that is hot all the time. On pole B is the same circuit, but the LINE input is behind a timer. The pilot light only works when pole B is not hot.

To clarify, both poles on the switch are connected to the same 120V load center circuit, same transformer leg: The voltage between the LINE side screws is zero when both are energized.

I have some 1201-PL switches that have a neutral terminal, so I was surprised to see that the 1222-PLG has no neutral screw; Only two LINE and two LOAD screws.

I verified that I've got the LINE and LOAD conductors hooked up as specified.

The Leviton cut sheet says only that "Pilot light switches require a neutral wire". There was no data sheet enclosed with the switch.

I don't know how the pilot light is connected to the two poles. If I reverse the wires on one pole, the pilot light does not work at all. Any suggestions?
 

Last edited by ArgMeMatey; 07-12-09 at 01:49 PM. Reason: Update
Sponsored Links
  #2  
Old 07-12-09, 06:24 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 36 Votes on 28 Posts
The Leviton on-line catalog doesn't really like that part number but I was able to find this drawing. It appears that the switch you have is for a 240 volt application. I suspect that the pilot lamp is lighting in your installation "when there is no power to one "pole" because then (and only then) do you have a voltage difference between the two lamp leads.

Workaround? I don't think there is one for this switch in your application. Sorry.
 
  #3  
Old 07-12-09, 07:30 PM
A
Member
Thread Starter
Join Date: Oct 2005
Location: Milwaukee WI
Posts: 1,339
Received 0 Votes on 0 Posts
That diagram looks about right. The yoke is stamped 20A 120-277 Volts, and I special-ordered it based on the catalog info regarding the neutral conductor, so I am disappointed. I sent an e-mail to Leviton and I would guess they will confirm your info.

Maybe a workaround would be to put the timer pole on a different circuit and turn this into a multiwire, but that seems a little extreme.

Thanks.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: