Want to run 220 volt to workshop
Hi,
I want to run 220 volt, 50 amp cable to a workshop that is about 150 feet away from the house. Can you tell me what cable to use, and anything to look out for?
Thanks
tabriz
I want to run 220 volt, 50 amp cable to a workshop that is about 150 feet away from the house. Can you tell me what cable to use, and anything to look out for?
Thanks
tabriz
#10
You would need to set a subpanel to power the shed. Only one circuit is allowed code-wise to feed your outbuilding.
This might mean increasing the size of the feeder to the shed.
This might mean increasing the size of the feeder to the shed.
#11
I want to run 220 volt, 50 amp cable to a workshop that is about 150 feet away from the house
#14
Member
Join Date: Jun 2007
Location: Ludlow, MA
Posts: 172
Received 0 Votes
on
0 Posts
the cheapest/most effective way to do this would be to run aluminum feeders, as you would a house. #2 aluminum with nolox is good for 100 amp subpanel. This is what I do for any garage that wants more then a simple 110v circuit to run a sander or sawzall.
Aluminum, you can only use for feeders. So you would have to feed a sub panel, Which is your smartest bet anyway. You can get both 110v and 220v. Plus you can have several circuits. For general receptacles, welders, a big honkin air compressor, a lift.
What you need to do is dig a 18" trench, run 2 inch conduit, and pull number 2 aluminum triplex. Also take into consideration if your ever going to want cable tv, alarm or telephone in this building. This would be the time to bury a 1" seperate plastic conduit right along side the 2 inch. Its cheap, and you can leave it there until your ready to pull low voltage though it. The low voltage and line voltage have to be in seperate conduits.
All this is assuming you have a 200amp main panel. If you only have 100amp, I would recommend a 60 amp subpanel and just dealing with the lights that will be dimming.
Aluminum, you can only use for feeders. So you would have to feed a sub panel, Which is your smartest bet anyway. You can get both 110v and 220v. Plus you can have several circuits. For general receptacles, welders, a big honkin air compressor, a lift.
What you need to do is dig a 18" trench, run 2 inch conduit, and pull number 2 aluminum triplex. Also take into consideration if your ever going to want cable tv, alarm or telephone in this building. This would be the time to bury a 1" seperate plastic conduit right along side the 2 inch. Its cheap, and you can leave it there until your ready to pull low voltage though it. The low voltage and line voltage have to be in seperate conduits.
All this is assuming you have a 200amp main panel. If you only have 100amp, I would recommend a 60 amp subpanel and just dealing with the lights that will be dimming.
#15
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,807
Received 0 Votes
on
0 Posts
the cheapest/most effective way to do this would be to run aluminum feeders, as you would a house. #2 aluminum with nolox is good for 100 amp subpanel. This is what I do for any garage that wants more then a simple 110v circuit to run a sander or sawzall.
Aluminum, you can only use for feeders. So you would have to feed a sub panel, Which is your smartest bet anyway. You can get both 110v and 220v. Plus you can have several circuits. For general receptacles, welders, a big honkin air compressor, a lift.
What you need to do is dig a 18" trench, run 2 inch conduit, and pull number 2 aluminum triplex. Also take into consideration if your ever going to want cable tv, alarm or telephone in this building. This would be the time to bury a 1" seperate plastic conduit right along side the 2 inch. Its cheap, and you can leave it there until your ready to pull low voltage though it. The low voltage and line voltage have to be in seperate conduits.
All this is assuming you have a 200amp main panel. If you only have 100amp, I would recommend a 60 amp subpanel and just dealing with the lights that will be dimming.
Aluminum, you can only use for feeders. So you would have to feed a sub panel, Which is your smartest bet anyway. You can get both 110v and 220v. Plus you can have several circuits. For general receptacles, welders, a big honkin air compressor, a lift.
What you need to do is dig a 18" trench, run 2 inch conduit, and pull number 2 aluminum triplex. Also take into consideration if your ever going to want cable tv, alarm or telephone in this building. This would be the time to bury a 1" seperate plastic conduit right along side the 2 inch. Its cheap, and you can leave it there until your ready to pull low voltage though it. The low voltage and line voltage have to be in seperate conduits.
All this is assuming you have a 200amp main panel. If you only have 100amp, I would recommend a 60 amp subpanel and just dealing with the lights that will be dimming.
If the OP is on 2005 or later NEC code cycle there are few issue it will affect the conductor rating the #2(35mm²) AL SER conductors they are only good for 90 amp even you run the THWN Alum verison sometime we called XLP { this item is restricted to outdoor only } that still on 90 amp max due the tempture rating on the conductor.
I know you will say something about this but if you have NEC codebook you will see why they derated this conductor / cable assambly as feeder circuit that you have to follow 60°C rating even thru the conductors are good for 90°C rating but if you run THHN/THWN copper conductors then you can get by with 75°C rating
The other thing If I did not catch what location where the OP is from some states you required to bury the conduit or cable at least 24 inch deep { I know in State of Wisconsin do require cable to be at least 24 inch but in rigid conduit ( both plastic and steel verison ) you can get by with 18 inches but for myself just stick with 24 inches and it will have no issue with it.
Also I wrote underline the triplex is no longer allowed with new subpanel feeds you will need 4 conductor type which it will have two active{ live } conductors and netrual and ground conductor.
The min size with 4- #2AWG conductors is 1.5 inches { really some case you can sqeak by with 1.25 inch conduit but not worth it espcally if you have more than two 90° ells there }
Merci,Marc