Wacky Voltage Problem

Reply

  #1  
Old 07-22-09, 08:28 AM
Member
Thread Starter
Join Date: Jul 2009
Location: Florida
Posts: 1
Received 0 Votes on 0 Posts
Wacky Voltage Problem

Trying to help a friend with an interesting problem. She lives in an old house in St Petersburg, FL, with a relatively modern circuit breaker panel. About a week ago, ceiling light fixtures in 4 rooms stopped working. I assumed it was simply the circuit breaker, but it turned out that is not the problem.

Here is what I do know:

The ceiling lights were working until recently.

Output from circuit breaker is 110v as expected

I checked the voltage at eack of the wall switches that control the ceiling lights, and the voltage at the four switches ranges from 7 to 13 volts.

I am guessing there is a single cable with a pigtail to each wall switch.

At each wall switch box there are two paper insulated wires tied to the switch. There is no ground wire or any other wires in the light switch box.

What is the likely cause of this low voltage problem?
 
Sponsored Links
  #2  
Old 07-22-09, 08:45 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Voltage checks at the switch usually don't mean much. If you were using a digital meter nothing. Since only two wires at the switch the power almost certainly comes in at the fan. At the fan is where you need to check. Most likely a loose wire nut connection.
 
  #3  
Old 07-22-09, 09:04 AM
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 8,629
Received 0 Votes on 0 Posts
I'd identify everything on that one circuit. And if outlets are also on it, I'd check outlets as well, for loose connection and/or for backstab connections.- since the (bad)outlet may then be feeding those ceiling boxes.

Also make sure that all the wire connections, including neutral, for this circuit, are tight in the panel box on both the breaker and the neutral buss.
 
  #4  
Old 07-22-09, 07:02 PM
Member
Join Date: Jul 2009
Location: so cal
Posts: 283
Received 0 Votes on 0 Posts
check 1st box in run

i'ld check the first ceiling box in the first room of the four rooms, i'ld suspect a loose wire nut on either the hot or the nuetral, and would also check the nuetral at the bus. you don't have aluminum wiring do you?
 
  #5  
Old 07-22-09, 08:56 PM
Member
Join Date: Jun 2007
Location: Ludlow, MA
Posts: 172
Received 0 Votes on 0 Posts
I think 7 to 13 volts probably means 0 volts. Its being generous. There is no power there. You have a bad connection somewhere on the circuit.
 
  #6  
Old 07-23-09, 08:05 AM
Banned. Rule And/Or Policy Violation
Join Date: May 2007
Location: Wisconsin
Posts: 8,629
Received 0 Votes on 0 Posts
I think kd went to the beach. . It be fun to learn where the problem was.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: