sub-panel wire size

Hi all,

I recently had my electrical service upgraded to 200A, as I've added a second floor addition. In the interest of not having to run a bunch of wires from the space of the new addition down through the walls and into the basement service panel, I plan to add a 100A sub-panel in the addition that will be fed from the main panel. I'm curious what size wire you would suggest feed the sub-panel. The distance between the two panel will approx. 15-feet.

Thanks!
 
  #2  
Old 08-11-09, 07:47 AM
R
Member
Join Date: Feb 2009
Location: Iowa
Posts: 339
Received 0 Votes on 0 Posts
Are you going to run this in conduit or SER wire?
Thanks!
JimBeer 4U2
 
  #3  
Old 08-11-09, 08:00 AM
H
Member
Thread Starter
Join Date: Aug 2009
Location: MN
Posts: 69
Received 0 Votes on 0 Posts
At this point, I'm anticipating running it through conduit along the outside of the house.
 
  #4  
Old 08-11-09, 08:11 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,941
Received 44 Votes on 42 Posts
Through conduit I would recommend copper THHN wire in #3 for the hots and neutral and #8 green or bare for the ground. The minimum size conduit you can use for these wires is 1", however 1-1/4" will probably be better if there are any bends or LB fittings to pull through.

Do you have a good subpanel location? Clearance can sometimes be tough to get in a second floor.
 
  #5  
Old 08-11-09, 08:50 AM
H
Member
Thread Starter
Join Date: Aug 2009
Location: MN
Posts: 69
Received 0 Votes on 0 Posts
Thanks for the suggestion As far as location of the sub-panel, I have plenty of options thankfully. The house addition I had built is a shell-only, so I'll be doing all the interior/finishing work. Therefore, the walls are currently open and 2x6 construction which leaves many location options. I will likely need an LB fitting, so 1.25" conduit may be the better choice for ease/convenience.

Thanks again!
 
  #6  
Old 08-11-09, 10:53 AM
R
Member
Join Date: Feb 2009
Location: Iowa
Posts: 339
Received 0 Votes on 0 Posts
As ibpooks quoted #3 would be the wire. Just so you know it's hard in some places to find #3 wire and if you can't then go with #2 copper.

Jim
 
  #7  
Old 08-11-09, 06:14 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 6,211
Received 298 Votes on 266 Posts
Originally Posted by H8Mondays View Post
As far as location of the sub-panel, I have plenty of options thankfully.
Just remember that you need a 'refrigerator box' area in front of the panel. Clearance 30" left to right, 36" in front, and 6' 6" tall. Also remember it can't be in a clothes closet or in a bathroom.
 
 