Branch circuit with no ground wire

I have a 20a circuit in my garage that powers all of the outlets. Whoever ran it, only used two wire 12awg with no ground. Short of completely re-running it, would it be OK to splice the neutral into the grounding lug on the outlets? I know this definitely wouldn't be up to code, but I'm wondering if it would be safer than no ground at all.
 
Sponsored Links
  #2  
Old 08-30-09, 11:45 AM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,482
Received 25 Votes on 19 Posts
No, NO and NO! There is only one place where neutral and equipment ground can be connected and that is at the Service (main) panel.

Install A GFCI receptacle in the first receptacle in the circuit and connect the rest of the circuit to the LOAD terminals in the GFCI. Mark all receptacles with the included stickers that read No Equipment Ground.
 
  #3  
Old 08-30-09, 11:46 AM
Member
Join Date: Aug 2008
Location: Kansas
Posts: 233
Received 0 Votes on 0 Posts
Originally Posted by mears View Post
I have a 20a circuit in my garage that powers all of the outlets. Whoever ran it, only used two wire 12awg with no ground. Short of completely re-running it, would it be OK to splice the neutral into the grounding lug on the outlets? I know this definitely wouldn't be up to code, but I'm wondering if it would be safer than no ground at all.
Furd tells you correctly...

..consider this ...the neutral or grounded conductor in a 120 volt branch circuit is a current carrying wire. If you connect your ground to it then you just energized your ground pin/terminal of the receptacle. Then you come along and plug a cord into the receptacle to operate an appliance. Now the ground wire in the power cord lets the neutral current flow to the metal of the appliance frame. Now you touch the metal of the appliance....get the picture??

Neutral is rarely allowed to be connected to ground load side of the main panel/service equipment for this reason and it is behind a metal door that keeps you from getting in contact with that bonding.

What you describe doing is called a bootleg ground and is highy dangerous to human safety.
 
  #4  
Old 08-31-09, 09:44 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Originally Posted by mears View Post
I'm wondering if it would be safer than no ground at all.
It is actually quite a bit less safe than leaving it with no ground.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: