Arc Fault CB-?? Neutral

Installing arc fault cb and the neutral doesn't reach the other side if the CB box.
Is it legal to pigtail an extended neutral in the box??
I dont want to reconfigure the panel to accomodate installation.
Thanks
BobH
 
Sponsored Links
  #2  
Old 09-03-09, 06:06 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,259
Received 103 Votes on 96 Posts
Absolutely. The panel is just like any other box, go ahead and add a pigtail and wire nut to extend your neutral.

Of course, make sure you use a white wire and a wire of the same (or larger) gauge.
 