Dayton 2yu66
Old 09-26-09, 08:41 PM
Question Dayton 2yu66
I AM TRYING TO INSTALL A DAYTON 2YU66 ELECTRICAL HEATER IT HAS THE OPTION OF 240/208V SINGLE OR THREE PHASE AND A 7.5/5.6kW RATING. THE FACTORY HAS IT SET FOR SINGLE PHASE. WHAT SIZE WIRE DO I CONNECT AND WHATCIRCUIT BREKER? i AM INSTALLING IT IN MY DETACHED 2.5 CAR GARAGE. THANKS
Old 09-26-09, 10:44 PM
Luana's Avatar
Number 8 AWG wire and a 40 ampere circuit breaker. You will need a local disconnect if the heater is more than 50 feet from the panel or not in direct line of sight of the panel.
Old 09-27-09, 05:39 AM
Red face
Thanks Luana! You mentioned a local disconnect. Do I install the double 40 breaker at both the main panel and the local disconnect? Also the directions only call for two hot and no neutral is that correct?
Old 09-27-09, 09:14 AM
ray2047's Avatar
Received 13 Votes on 11 Posts
An unfused disconnect is fine. A 60 amp AC unfused disconnect is a good cheap option. No neutral is used on 240v.
Is this an attached or detached garage. If it is detached you will almost certainly need a subpanel. If attached, local code permitting*, you can use 8-2 Romex.
*If Chicago code may vary from NEC.
P.S. Glad you got your caps lock fixed. Just can't take shouting this early.