UF Question

I think I know the answer but on the outside chance I'm wrong can UF be run overhead supported by a messenger. I'm guessing unprotected and UV will be in your condemnation but I just wanted to be sure.
 
  #2  
Old 09-30-09, 10:15 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,942
Received 44 Votes on 42 Posts
UF-B can be used overhead supported by a messenger as long as it is marked UV resistant by the mfgr. 340.12(11) and 396(II)
 
  #3  
Old 09-30-09, 10:43 PM
ray2047's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
Bingo! UF-B sunlight resistant. I got the cable for the perfect price so I have a project in my future. Would 1/8" plastic coated steel cable be adequate for a messenger? The distance is 20 feet. I assume the messenger should be grounded?

My DUH moment for the day. I didn't check to see if it was sunlight resistant before posting. So use to thinking of it as underground cable figured it wouldn't be.

Thank you for your help.
 

Last edited by ray2047; 09-30-09 at 11:54 PM.
  #4  
Old 09-30-09, 11:06 PM
F
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,807
Received 0 Votes on 0 Posts
Yes Ray you have to ground the messenger cable in case something go wrong with UF cable and Ibpooks mention sunlight restanice that is the key word if not sunlight restanice it will break apart in pretty short time.

Merci,Marc
 
  #5  
Old 09-30-09, 11:53 PM
ray2047's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
Again thanks.

...................
 
  #6  
Old 10-01-09, 08:19 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,942
Received 44 Votes on 42 Posts
The 1/8" steel cable should be fine to support the UF. I would hope you don't have to worry about cable ice load on the gulf coast! Tie the messenger in with the ground at the weatherhead -- compression connectors hold up better outdoors than wirenuts.
 
  #7  
Old 10-01-09, 09:41 AM
ray2047's Avatar
Member
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 33,581
Received 13 Votes on 11 Posts
Perhaps I should have said no ice load. Yes, split bolt.
 
 