Can load side disconnect be smaller than "sub" panel disconnect?

Can load side disconnect be smaller than "sub" panel disconnect?

Reply

  #1  
Old 11-02-09, 01:40 PM
B
Member
Thread Starter
Join Date: Nov 2009
Location: Remote Alaska
Posts: 2
Received 0 Votes on 0 Posts
Can load side disconnect be smaller than "sub" panel disconnect?

I recently bought a 100A meter/main disconnect, but it seems no one readily sells 100A panels, so I bought a 125A Square-D HOM style panel. This is all to wire a newly constructed storage building. My question is: can the interior panel "main breaker" be larger than the outside service disconnect? I will probably have one 240v outlet inside just in case, but don't really anticipate much loading -just lights & misc hand tools.
 
Sponsored Links
  #2  
Old 11-02-09, 01:50 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
The main breaker on a subpanel serves primarily as a disconnect switch. Protection is provided by the breaker at the main panel so the answer is yes the subpanel breaker can be larger. It is just a switch in this configuration.
 
  #3  
Old 11-02-09, 02:42 PM
B
Member
Thread Starter
Join Date: Nov 2009
Location: Remote Alaska
Posts: 2
Received 0 Votes on 0 Posts
Originally Posted by ray2047 View Post
The main breaker on a subpanel serves primarily as a disconnect switch. Protection is provided by the breaker at the main panel so the answer is yes the subpanel breaker can be larger. It is just a switch in this configuration.
Thanks Ray. So just to clarify, the interior 125A main breaker is basically just an expensive switch for that panel and the overload protection is handled by the exterior 100 amp main disconnect breaker/switch?
 
  #4  
Old 11-02-09, 03:06 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Originally Posted by bushdude View Post
Thanks Ray. So just to clarify, the interior 125A main breaker is basically just an expensive switch for that panel and the overload protection is handled by the exterior 100 amp main disconnect breaker/switch?
Yes.

..............................
 
  #5  
Old 11-02-09, 03:07 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
Yes that is correct. Overcurrent protection is provided by the smallest breaker in the feeder.
 
  #6  
Old 11-02-09, 03:36 PM
R
Member
Join Date: Feb 2009
Location: Iowa
Posts: 339
Received 0 Votes on 0 Posts
Also remember that you will be able to size your wire based on that 100 amp breaker and not the 125 amp in your panel box.

Thanks!
Jim

 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: