sub panel questions- thhn and gray pipe

Hi to all,

I plan on running #6 THHN thru gray pipe to my garage 90 feet away for a 50A subpanel. I plan on connecting the gray pipe from the main to the sub panel. Can I run the gray pipe along the out side of my foundation wall( which is underneath my deck) until I get to the end of my house and then down 24" in the ground to the garage?

Thanks, JB
 
Sponsored Links
  #2  
Old 11-16-09, 08:33 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,944
Received 30 Votes on 26 Posts
Yes, as long as the conduit is properly strapped within 3' of each termination and no more than 3' between straps. You may need to consider an expansion fitting where subject to ground movement from frost heave.

You need to use THWN in an exterior and underground application. THHN is only for interior usage. Most THHN will be dual rated THHN/THWN but check before purchase.

Where subject to physical damage Schedule 80 PVC would need to be used.

You will also need a grounding system at your outbuilding.
 

Last edited by ibpooks; 11-16-09 at 09:26 AM.
  #3  
Old 11-16-09, 10:57 AM
Member
Thread Starter
Join Date: Jan 2005
Location: NJ
Posts: 84
Received 0 Votes on 0 Posts
Thanks PCB,

I have another question about the ground. An electrian told me that I could use #10 ground wire instead of #6 but I need an 8ft ground rod at the garage sub panel. Is that true?

thanks, JB
 
  #4  
Old 11-16-09, 12:04 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
A #10 copper ground green or bare only is fine with #6 copper. Yes you need an 8 foot ground wire to comply with 2008 NEC.

See: http://forum.doityourself.com/electr...-drawings.html
 
  #5  
Old 11-17-09, 03:15 PM
Member
Thread Starter
Join Date: Jan 2005
Location: NJ
Posts: 84
Received 0 Votes on 0 Posts
Thank you Ray for your help on this. JB
 
  #6  
Old 11-17-09, 05:35 PM
Member
Join Date: Feb 2009
Location: Iowa
Posts: 339
Received 0 Votes on 0 Posts
Originally Posted by Jethro buckeye View Post
Hi to all,

I plan on running #6 THHN thru gray pipe to my garage 90 feet away for a 50A subpanel. I plan on connecting the gray pipe from the main to the sub panel. Can I run the gray pipe along the out side of my foundation wall( which is underneath my deck) until I get to the end of my house and then down 24" in the ground to the garage?

Thanks, JB
I don't what to throw you a curve in this but you can use #8 wire on this 50 amp sub panel if your are using THHN/THWN wire the complete way. As long as your termials on the breakers or lugs are rated for 75c you're good. It could save you some money.

Thanks!
Jim

 
  #7  
Old 11-17-09, 06:01 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Along that same vein, if you stick with the #6 you can increase the breaker to 60A.
 
  #8  
Old 11-17-09, 08:32 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,965
Received 59 Votes on 52 Posts
Originally Posted by ray2047 View Post
A #10 copper ground green or bare only is fine with #6 copper.
If you run the pipe outside then the ground can only be insulated. Not bare.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: