I am running additional circuits to some bedrooms in my house. I was given 3 - 100' rolls of 12/2 wire. What I would like to know is if it is permissable to use 12/2 wire on a 15 amp circuit?
 
  #2  
Old 11-27-09, 12:39 AM
ARC-N-SPARK's Avatar
Member
Join Date: Mar 2008
Location: Northern IL
Posts: 85
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, you can use #12 on a 15A circuit.
 
  #3  
Old 11-27-09, 01:10 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Since you have the wire already just install a 20 amp breaker and get 1/3 more capacity for no additional cost.
 
  #4  
Old 11-27-09, 04:27 AM
J
Member
Join Date: Oct 2006
Location: Wilmington
Posts: 3,994
Upvotes: 0
Received 0 Upvotes on 0 Posts
Keep in mind that all J-boxes must fit the size of the wire, regardless of derating the circuit. If you are using old or existing boxes, they are likely too small. NEC 314.16

And a bedroom circuit may require an AFCI breaker, check local code.
 
 