Hair dryer- blowing circuit breaker
When I use my hair dryer, all is fine. When I return to use it, the outlet is not working and I must reset the circuit breaker. An electrician replaced the outlet and the circuit breaker - the problem still persists. (Same problem with old hair dryer, this one is new -uses 13 amps) Any ideas?
#3
Member
Join Date: Nov 2004
Location: USA
Posts: 1,823
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'm assuming this is a GFCI?Or are you resetting the breaker at the breaker box?
Hair dryers have a heating element which is one of the heavier electrical draws just like a space heater etc plus it is drawn in a burst of use when you turn it on.
and if this is a 15 amp circuit and you're pulling 13 that doesn't leave much wiggle room.
Hair dryers have a heating element which is one of the heavier electrical draws just like a space heater etc plus it is drawn in a burst of use when you turn it on.
and if this is a 15 amp circuit and you're pulling 13 that doesn't leave much wiggle room.
#5
Member
Thread Starter
Join Date: Jun 2005
Location: Michigan
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
hair dryer -blowing circuit breaker
The outlet is not a GFCI, although the hair dryer has its own button which does not trip. There is a toothbrush charger on the same socket. It is 15 amp. I am resetting the breaker at the box. Thanks.
#6
Surprised the electrician didn't tell you that the bathroom must be a 20a circuit GFCI protected. You need to run a new circuit just for the receptacle. 12-2 NM-b on a 20a circuit. Use a GFCI receptacle (cheapest method) or GFCI breaker. Under grandfathering you may be able to leave the existing receptacle but it needs to be changed to GFCI. You could use the 15a for small loads like a radio or tooth brush.
#7
Member
Join Date: Nov 2004
Location: USA
Posts: 1,823
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes I'd change to a GFCI.I suspect this is an older home,sure sounds like it.More than likely if you keep using this circuit for the hair dryer this problem will continue and eventually wear out the breaker.At least a GFCI might trip right there and make it easier to deal with.That too would eventually wear out but be easier to replace.I don't really see this as a dangerous situation assuming there isn't anything else going on like a short,old damaged wiring etc but it will be an annoyance.Probably only a rewire of the circuit will eliminate it.
#10
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Guys, please understand that the requirement for 20 ampere circuits serving only bathrooms is less than 20 years old. My house was built in 1987 and has one 15 ampere circuit (#14 type NM cable) that originally served the garage outlet (which contained the only GFCI on the circuit) garage door opener, a single duplex receptacle in each of two bathrooms and the outside receptacle on the back deck.
There are probably hundreds of thousands of existing bathroom receptacle circuits that were wired BEFORE the requirement of dedicated 20 ampere circuits but after the requirement of GFCI on bathroom receptacle circuits. Unless a major renovation has taken place in the bathroom these circuits are still code compliant although I agree it is best to upgrade them to current code when possible.
There are probably hundreds of thousands of existing bathroom receptacle circuits that were wired BEFORE the requirement of dedicated 20 ampere circuits but after the requirement of GFCI on bathroom receptacle circuits. Unless a major renovation has taken place in the bathroom these circuits are still code compliant although I agree it is best to upgrade them to current code when possible.
#11
Yes I'd change to a GFCI .I suspect this is an older home,sure sounds like it .More than likely if you keep using this circuit for the hair dryer this problem will continue and eventually wear out the breaker. At least a GFCI might trip right there and make it easier to deal with. That too would eventually wear out but be easier to replace. I don't really see this as a dangerous situation assuming there isn't anything else going on like a short,old damaged wiring etc but it will be an annoyance. Probably only a rewire of the circuit will eliminate it.
#12
I would advise you to check the connections either at the receptacle just ahead of this one or where the hair dryer is plugged in. There may be an poor connection that is heating up and opening under load.
#13
My house was built in 1987 and has one 15 ampere circuit (#14 type NM cable) that originally served the garage outlet (which contained the only GFCI on the circuit) garage door opener, a single duplex receptacle in each of two bathrooms and the outside receptacle on the back deck.