wire size for electric heater in air handler
Old 12-13-09, 05:43 PM
Hello all,
I am installing a 10kw 220v heater strip in my air handler to give back up heat for the heat pump. The manufacture requires 60 amp breaker in the panel. I want to know what size wire should I run from the panel to the air handler, its about a 25' run. I think #6 will work but wanted to make sure that that is okay.
I calculated the amps to be 41.66 for the heater and over current protection for that would be 52 amps, thus the 60 amp breaker. And the #6 wire is rated for 55 to 60 amps. Would this be okay or is this to close?
Also, if I have to use #4 could I run 2 #10 wires for each phase (4 wires total plus a ground) instead of the single #4 for each phase.
Thanks, MRT19
Old 12-13-09, 06:00 PM
F
Received 35 Votes on 27 Posts
Since heating circuits must be designed to 125% of full-load the #6 is fine along with the 60 ampere circuit breaker. The 25 foot distance does not require any upsizing for voltage drop. You may NOT parallel anything smaller than 1/0 conductors for field wiring.
Old 12-13-09, 06:55 PM
F
The 16mm˛{ #6 } will work but a nice gotcha is are you running with SE cable or THHN/THWN in conduit ?
That may affect the rating but due both are copper I think you should not have any issue with it.
Unforetally you can not parallel any conductor smaller than 55mm˛ { #1/0 }any larger then it is not a issue
Merci.
Marc