Crouse-Hinds E26095 Panel - need grounding bar

I have an old 100A panel and I'd like to add an equipment grounding bar. I can't find the part anywhere on the internet, so I'm sure it is no longer manufactured.

Local Lowes has several grounding bars, but hole spacing is not right. Closest is the Eaton Cutler Hammer with panel screws spaced 1.75" apart. It looks like the panel needs 2".

Are there any companies that might carry this?

Thanks,

Bill
 
Sponsored Links
  #2  
Old 12-14-09, 02:36 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
In this case, I would find the one that is close enough and drill/tap a screw hole where needed. Code allows drilling and tapping metal boxes for grounding purposes. The main issue is that you cannot use a piercing screw like a sheet metal screw, but it must have machined threads. Self-tapping is okay as long as the hole is drilled the right size for it to bite into the metal.
 
  #3  
Old 12-14-09, 06:35 PM
B
Member
Thread Starter
Join Date: Nov 2009
Location: Illinois
Posts: 7
Received 0 Votes on 0 Posts
Thanks, glad to know this can be done. What a time saver!
 
  #4  
Old 12-14-09, 06:54 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,150
Received 87 Votes on 74 Posts
I would not think a self tapping screw would have the required 2 thread minimum.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: