Dual-pole GFCI Breakers used in 220 circuits

I was reading about installing GFCI breakers in panels. You connect the nuetral from that circuit to the breaker along with the hot and then the pigtail white from breaker to nuetral panel.

So, if I do a 220, dual pole circuit (2 hots and a ground where there is no nuetral connected) how is circuit GFCI protected??? AM I thinking about this the wrong way?
 
Sponsored Links
  #2  
Old 12-16-09, 09:43 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
Originally Posted by sandyharry View Post
AM I thinking about this the wrong way?
If there is no neutral used by the load, then no neutral needs to be connected to the GFCI breaker. The pigtail from the GFCI breaker to the neutral bus still needs to be connected though.

The function of the GFCI is not impaired by the lack of neutral if that's what you're asking.

I assume this question is a follow-on from the pier project, so a neutral would be used in that case because of the lights and other general-purpose loads on the multiwire circuit. Only the boatlift would not have a neutral connected as it is a straight 240V device.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: