Siemens GFCI / AFI Combo?
#1
Member
Thread Starter
Join Date: Mar 2007
Location: Greenfield, WI
Posts: 26
Received 0 Votes
on
0 Posts
Siemens GFCI / AFI Combo?
Hello,
I am replacing my load center with a Generac Genready panel which utilizes Siemens breakers. While I know CH makes a GFCI/AFI combo breaker does anyone know if Siemens (or Siemens compatible) does?
I am replacing my load center with a Generac Genready panel which utilizes Siemens breakers. While I know CH makes a GFCI/AFI combo breaker does anyone know if Siemens (or Siemens compatible) does?
Sponsored Links
#2
Member
Join Date: Oct 2008
Posts: 1,312
Received 0 Votes
on
0 Posts
Is it an AFCI breaker which is called a "combination breaker"?
Does it says anywhere on the breaker packaging or documentation GFCI?
Or does it just use the word "combination"?
If just the word "combination" is used, then this is a specific type of AFCI breaker and not also a GFCI.
Does it says anywhere on the breaker packaging or documentation GFCI?
Or does it just use the word "combination"?
If just the word "combination" is used, then this is a specific type of AFCI breaker and not also a GFCI.
#3
Forum Topic Moderator
Here are the basic categories. What combination of functions exactly are you looking for?
1) parallel arc AFCI also called a branch/feeder (70A protection) AFCI, generally permitted under the 2002 and 2005 NEC. Siemens part no. Q115AF (15A) Q120AF (20A)
2) series arc AFCI (5A protection) sold as a "Combination AFCI" because it provides both series and parallel arc protection. Required by 2008 NEC. Siemens Q115AFC (15A) Q120AFC (20A).
3) Class A GFCI "Personnel Protection" (5mA) -- required for bathroom, kitchen, outdoors, etc. Siemens QF115
4) GFCI "Equipment Protection" (30mA) -- for added fire/shock safety but not adequate for protection of people. QE115
All AFCI breakers provide #4, most new AFCI breakers provide #2 which includes #1 and #4. I don't think there's a Siemens breaker that provides both #2 and #3. Most of these listed have other amperages and available in 2 pole versions.
1) parallel arc AFCI also called a branch/feeder (70A protection) AFCI, generally permitted under the 2002 and 2005 NEC. Siemens part no. Q115AF (15A) Q120AF (20A)
2) series arc AFCI (5A protection) sold as a "Combination AFCI" because it provides both series and parallel arc protection. Required by 2008 NEC. Siemens Q115AFC (15A) Q120AFC (20A).
3) Class A GFCI "Personnel Protection" (5mA) -- required for bathroom, kitchen, outdoors, etc. Siemens QF115
4) GFCI "Equipment Protection" (30mA) -- for added fire/shock safety but not adequate for protection of people. QE115
All AFCI breakers provide #4, most new AFCI breakers provide #2 which includes #1 and #4. I don't think there's a Siemens breaker that provides both #2 and #3. Most of these listed have other amperages and available in 2 pole versions.
#4
Member
Thread Starter
Join Date: Mar 2007
Location: Greenfield, WI
Posts: 26
Received 0 Votes
on
0 Posts
And...
Thanks! I am someone who would rather overdo things than under do them and regret it later -- while NEC does not require GFCIs on the Dishwasher/Fridge/Disposal circuits, would I be better served/protected putting these dedicated circuits on a AFI or GFCI?
Also -- is there anything barring me from running certain circuits to simplex outlets connected to a few large UPSs(outlet circuits of course)? We have a standby generator but it takes ~1min to power up and I dispise blinky lights (or football interruptions!). I have a few 3000VA (2500W) UPSs intended for this purpose.
Also -- is there anything barring me from running certain circuits to simplex outlets connected to a few large UPSs(outlet circuits of course)? We have a standby generator but it takes ~1min to power up and I dispise blinky lights (or football interruptions!). I have a few 3000VA (2500W) UPSs intended for this purpose.
#5
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,808
Received 0 Votes
on
0 Posts
Normally the Fridge is on GFCI circuit but it will be much wiser to keep it seperated circuit if that possible
For hardwired dishwasher and garbage dispoal I don't think they required GFCI unless the local code require it.
IMO for myself I will just add a GFCI breaker or faceless GFCI receptale and that way it will meet the code no question asked.
However with hardwired verison you will have to add a local disconnection anyway a simple single pole toggle switch will meet this requirement.
UPS on AFCI most case it not much issue what I heard but when you switch over to generator mode it may not affect the generator itself but the UPS it will depending on the setting on the UPS itself plus how tight the speed reguation on the generator itself that is the key issue there. { that one reason why I only have diesel generators due they are very tight on speed regulation itself +- half hertz ( locked in 60 HZ so will have 591/2 to 601/2 HZ in my generators in USA side France side it will be just 10 HZ less than USA is due I have 50 HZ in France }
Merci.
Marc
For hardwired dishwasher and garbage dispoal I don't think they required GFCI unless the local code require it.
IMO for myself I will just add a GFCI breaker or faceless GFCI receptale and that way it will meet the code no question asked.
However with hardwired verison you will have to add a local disconnection anyway a simple single pole toggle switch will meet this requirement.
UPS on AFCI most case it not much issue what I heard but when you switch over to generator mode it may not affect the generator itself but the UPS it will depending on the setting on the UPS itself plus how tight the speed reguation on the generator itself that is the key issue there. { that one reason why I only have diesel generators due they are very tight on speed regulation itself +- half hertz ( locked in 60 HZ so will have 591/2 to 601/2 HZ in my generators in USA side France side it will be just 10 HZ less than USA is due I have 50 HZ in France }
Merci.
Marc
#6
Forum Topic Moderator
Also -- is there anything barring me from running certain circuits to simplex outlets connected to a few large UPSs(outlet circuits of course)?
#7
Member
Thread Starter
Join Date: Mar 2007
Location: Greenfield, WI
Posts: 26
Received 0 Votes
on
0 Posts
Thanks, I think I will leave dedicated kitchen circuits on normal breakers as you suggested.
For the "UPS" circuits, my solution was going to be add a small load center with each rail being serviced by one UPS. Since I will be only adding single pole breaks that shouldn't be a problem, and the UPS internally will trip if more that it's output is pulled. The goal of the load center is to be able to add combination AFI breakers on the service side. If I put the AFIs on the lines to the UPS I think when the UPS "conditions" the line it would defeat any benefits of the AFI supplying the UPS.
Any thoughts?
For the "UPS" circuits, my solution was going to be add a small load center with each rail being serviced by one UPS. Since I will be only adding single pole breaks that shouldn't be a problem, and the UPS internally will trip if more that it's output is pulled. The goal of the load center is to be able to add combination AFI breakers on the service side. If I put the AFIs on the lines to the UPS I think when the UPS "conditions" the line it would defeat any benefits of the AFI supplying the UPS.
Any thoughts?
#8
Forum Topic Moderator
Okay I understand the plan. The general idea here is to wire it just like you would with a standby generator panel, however you connect the UPS to the transfer switch inlet instead of a generator. Unless it is listed for the purpose, a UPS should not be hardwired so cords and inlets are required. You are correct that the UPS would defeat the upstream AFCI protection. I recommend that you contact the UPS manufacturer to get their position on AFCI breaker compatibility downstream of the UPS. My expectation is that it should work just fine as the UPS provides a better power source than the line does.
#9
Forum Topic Moderator
I was thinking about this a little more. Could you describe the use of the UPSs more? What are they powering? Is the issue just that you want them in a different room than the protected load or do you intend to power more with them?
#10
Member
Thread Starter
Join Date: Mar 2007
Location: Greenfield, WI
Posts: 26
Received 0 Votes
on
0 Posts
Thanks for your time thinking about this. Here is the plan:
200A Service to a Generac GenReady Load Panel. Everything to be on generator service (20kW genset).
Two dedicated 30A 120V circuits to two 3000VA (2500W) UPSs. Each UPS will have two connections (12gauge) to a small load center. This is due to the UPS only having NEMA 5-15R outlets, and of course I want to supply 20A circuits.
The reasoning for the UPSs is to offer continuous power during genset powerup (~1min). I want to offer every room socket to be on this backup as well as a central location for battery replacement.
Here is a simple diagram:
<30A 120V> |---------| <30A 120V>
|---------|
|---------|
O (UPS) O (UPS)
|-| -----|-| <-- (2) 12Ga Connections
|-| -----|-| via Simplex outlets
########
|-|------|-| <-- Each UPS Supplying
|-|------|-| one panel rail.
|-|------|-|
|-|------|-| <-- Each outlet circuit
######## protected by AFIC
Small Panel breaker.
200A Service to a Generac GenReady Load Panel. Everything to be on generator service (20kW genset).
Two dedicated 30A 120V circuits to two 3000VA (2500W) UPSs. Each UPS will have two connections (12gauge) to a small load center. This is due to the UPS only having NEMA 5-15R outlets, and of course I want to supply 20A circuits.
The reasoning for the UPSs is to offer continuous power during genset powerup (~1min). I want to offer every room socket to be on this backup as well as a central location for battery replacement.
Here is a simple diagram:
<30A 120V> |---------| <30A 120V>
|---------|
|---------|
O (UPS) O (UPS)
|-| -----|-| <-- (2) 12Ga Connections
|-| -----|-| via Simplex outlets
########
|-|------|-| <-- Each UPS Supplying
|-|------|-| one panel rail.
|-|------|-|
|-|------|-| <-- Each outlet circuit
######## protected by AFIC
Small Panel breaker.
«
Previous Thread
|
Next Thread
»