New range

I'm in the planning stages for a kitchen remodel and I'm reviewing all the electrical issues. The current range has a 3 wire(red, black, white) with all conductors insulated, but no bare ground. I'm assuming the white is serving as a neutral/ground. Assuming a new range will be 4 wire, is it acceptable to run a bare ground back to the panel that is separate from the 3 wire sheathed romex?
 
Sponsored Links
  #2  
Old 01-14-10, 01:00 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Your plan is acceptable; the ground wire should be green or bare #10 copper and should follow the same rules for fastening and protection as romex. The new range receptacle should be a NEMA 14-50R, and the range should have a NEMA 14-50P cord set installed and the internal bonding jumper removed per range installation manual.
 
  #3  
Old 01-14-10, 05:05 PM
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 140
Received 0 Votes on 0 Posts
Thanks for the response. Running a ground will be simpler than running a whole new circuit.
 
  #4  
Old 01-15-10, 10:27 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Just a note to future readers of this thread: the OP's situation is somewhat unique in that the existing circuit has three insulated wires (black, red, white). Many old range circuits have only two insulated wires (black, red or white, bare). This type of circuit cannot have a supplemental ground wire installed because the neutral would be uninsulated.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: