Breaker problem
#1
Member
Thread Starter
Join Date: Jan 2010
Location: Pennsylvania
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts

A 100A cutler hammer breaker burned out. The model number is a CH2100 breaker. However, when I went to purchase a CH2100 breaker, the breaker was only half the size of the one I was replacing. The guy at the electrical store said he had never seen a breaker this size. I don't think it is a main breaker because it doesn't look like the pics I found on the internet.
So my question is, can I use the normal sized CH2100 breaker in my panel? Or does anyone know what kind of breaker this is and where I can purchase a like for like replacement? I've included pictures of the breaker and my panel:
Yfrog Album
So my question is, can I use the normal sized CH2100 breaker in my panel? Or does anyone know what kind of breaker this is and where I can purchase a like for like replacement? I've included pictures of the breaker and my panel:
Yfrog Album
#2
The breaker you bought is a standard 2 pole 100 amp breaker. These would typically be used to fed another panel downstream from the service panel.
You need the 100 amp main breaker that is a different configuration as you found out. It looks like you need a CSR2100N breaker, but I would confirm this with a CH dealer. There may have been different configurations of the breaker over time. You may be able to find a part number on the main breaker itself.
You need the 100 amp main breaker that is a different configuration as you found out. It looks like you need a CSR2100N breaker, but I would confirm this with a CH dealer. There may have been different configurations of the breaker over time. You may be able to find a part number on the main breaker itself.
#3
Member
Thread Starter
Join Date: Jan 2010
Location: Pennsylvania
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I think my question is missing some info. I have 200A service to the main panel. The main breaker is not the issue. The breaker that burned out is a 100A breaker that feeds the heat pump, which is essentially a sub panel. The part number on the burned out breaker is CH2100, which is weird because the CH2100 at the store is half the size of the burned out breaker.
I think I only need a standard 2 pole 100A breaker. And it looks like it may fit. But I'd like confirmation because I'm not sure why the burned out breaker is so big.
PS: It also looks like the bus bars in my panel are off center. Is this normal?
I think I only need a standard 2 pole 100A breaker. And it looks like it may fit. But I'd like confirmation because I'm not sure why the burned out breaker is so big.
PS: It also looks like the bus bars in my panel are off center. Is this normal?
#4
Member
Join Date: Jul 2009
Location: so cal
Posts: 273
Upvotes: 0
Received 0 Upvotes
on
0 Posts
old CH 2100 Main
you got this breaker CH 2100 Main
CUTLER - HAMMER CH 2100 CH 2 POLE 100 AMP MAIN BREAKER - eBay (item 120445356354 end time Feb-02-10 06:40:41 PST)
and
Cutler-Hammer CH2100 100 Amp 2Pole Main Circuit Breaker - eBay (item 370310272025 end time Feb-20-10 09:08:40 PST)
I am not sure your panel allows for 100 amp below the main upper bus bars, like current CH panels do
A to Z breakers ( in Anaheim , CA ) would have one reconditioned ( not used ), as i get my old breakers from them. email them the photo and the can get one for you.
A to Z Circuit Breakers Inc. - New, Reconditioned, Obsolete, Hardware Kits.
good luck
CUTLER - HAMMER CH 2100 CH 2 POLE 100 AMP MAIN BREAKER - eBay (item 120445356354 end time Feb-02-10 06:40:41 PST)
and
Cutler-Hammer CH2100 100 Amp 2Pole Main Circuit Breaker - eBay (item 370310272025 end time Feb-20-10 09:08:40 PST)
I am not sure your panel allows for 100 amp below the main upper bus bars, like current CH panels do
A to Z breakers ( in Anaheim , CA ) would have one reconditioned ( not used ), as i get my old breakers from them. email them the photo and the can get one for you.
A to Z Circuit Breakers Inc. - New, Reconditioned, Obsolete, Hardware Kits.
good luck
#5
Member
Thread Starter
Join Date: Jan 2010
Location: Pennsylvania
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thank Mikerios. I can't believe you found it!
But what do you mean that you aren't sure my panel will allow for a 100A breaker below the main like the current CH panels? You mean a normal sized 100A breaker?
I think I will replace it, but I do wonder if the only reason that old breaker is in there is because someone was trying to use up their old parts. This is the house I intend to be in for the next 30-50 years so I suppose at some point I should get an electrician out here to redo the entire panel properly with new equipment.
But what do you mean that you aren't sure my panel will allow for a 100A breaker below the main like the current CH panels? You mean a normal sized 100A breaker?
I think I will replace it, but I do wonder if the only reason that old breaker is in there is because someone was trying to use up their old parts. This is the house I intend to be in for the next 30-50 years so I suppose at some point I should get an electrician out here to redo the entire panel properly with new equipment.
#6
Member
Thread Starter
Join Date: Jan 2010
Location: Pennsylvania
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
And another thought. It looks like one of the stabs from the bus bar is a little black. Should I clean the stabs before installing the new breaker? If so, what do I clean it with.
Thanks for the assistance.
Thanks for the assistance.
#7
If the buss stab is black it is probably from continued arcing. This may have affected its ability to make a good contact with the breaker. Poor connections will cause heat buildup. I would advise getting an electrician to look at this and evaluate it.
#8
Member
Join Date: Jul 2009
Location: so cal
Posts: 273
Upvotes: 0
Received 0 Upvotes
on
0 Posts
interesting breaker
current CH panels allow for 100 amp 2 pole breakers where the "normal" breakers would be, not the main breaker like you have, but have never seen a breaker like the one you have in that old of a CH panel. I have an old CH panel with tan breakers and a notch in the breaker on the top, on the panel there is a small bar with hold the breaker in place ( in addition to the springs at the base of the breaker which grip the bus bar tabs ). A to Z was the only place where I could find them ( and they are somewhat local to me ). Eventually I plan to change out the 100 amp panel for a 200 amp CH panel since this panel does not allow for ARC Fault breakers.
as for the bus tabs, yes, definitely clean them ,kill the power of course before you do so. a green scotch brite pads works well and should remove the carbon build up.
hopefully you do not have pitting on the tabs. but how much load is your heatpump drawing?
as for the bus tabs, yes, definitely clean them ,kill the power of course before you do so. a green scotch brite pads works well and should remove the carbon build up.
hopefully you do not have pitting on the tabs. but how much load is your heatpump drawing?
#9
Member
Thread Starter
Join Date: Jan 2010
Location: Pennsylvania
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The 100A bkr feeds my heat pump, which is essentially a sub panel consisting of 2 60A bkrs and one 30A bkr. That adds up to 150A. So the 100A bkr would routinely trip. I measured 105A coming from the heat pump. Once I figured out what was going on, I started to leave the 30A bkr tripped and didn't have a problem until recently. It did get very cold, although I didn't measure, I think it's possible that more than 100A was going through the bkr. Pcboss mentioned that the black on the stab could be from arcin, which makes since because that's where the bkr is burnt out. Maybe the bkr wasn't seated properly. My current plan is to buy a replacement bkr, clean the stab, and run the heat pump from here on out with one of the 60A bkrs tripped.
You mentioned that you've never seen a bkr like that in a panel that old. Do you think a normal 100A 2 pole CH bkr would fit? It kind of looks like it would line up.
You mentioned that you've never seen a bkr like that in a panel that old. Do you think a normal 100A 2 pole CH bkr would fit? It kind of looks like it would line up.
#10
A 100A cutler hammer breaker burned out. The model number is a CH2100 breaker. However, when I went to purchase a CH2100 breaker, the breaker was only half the size of the one I was replacing. The guy at the electrical store said he had never seen a breaker this size. I don't think it is a main breaker because it doesn't look like the pics I found on the internet.
So my question is, can I use the normal sized CH2100 breaker in my panel? Or does anyone know what kind of breaker this is and where I can purchase a like for like replacement? I've included pictures of the breaker and my panel:
Yfrog Album
So my question is, can I use the normal sized CH2100 breaker in my panel? Or does anyone know what kind of breaker this is and where I can purchase a like for like replacement? I've included pictures of the breaker and my panel:
Yfrog Album
#11
Member
Thread Starter
Join Date: Jan 2010
Location: Pennsylvania
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the info. About the heat pump, the 2 60A and 1 30A breakers are for the heat package, which comes on in stages when it's too cold for the heat pump. There is a separate 50A double pole breaker for the outside part. Oddly enough, that breaker is a normal sized double pole breaker. The house was built in 1979, so perhaps that large 100A breaker was a slightly older left over breaker they decided to use. Thanks for the explanation about the change in size of the CH 2100 breakers.
#12
Thanks for the info. About the heat pump, the 2 60A and 1 30A breakers are for the heat package, which comes on in stages when it's too cold for the heat pump. There is a separate 50A double pole breaker for the outside part. Oddly enough, that breaker is a normal sized double pole breaker. The house was built in 1979, so perhaps that large 100A breaker was a slightly older left over breaker they decided to use. Thanks for the explanation about the change in size of the CH 2100 breakers.
#13
Member
Thread Starter
Join Date: Jan 2010
Location: Pennsylvania
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yeah, you are correct, the 100A bkr is overloaded. The wire won't support anything larger. That's why I had been running the heat pump with the 30A bkr tripped off. But then the 100A bkr burned up on me the other day so once I get it fixed I'm going to leave the 60A bkr off. I was going to rewire the 150A ckt but the ac guy said my heat pump was putting out plenty of heat without it and that it would save money with one of the breakers tripped. But I was thinking it may just end up running longer and negate any savings.
#14
Yeah, you are correct, the 100A bkr is overloaded. The wire won't support anything larger. That's why I had been running the heat pump with the 30A bkr tripped off. But then the 100A bkr burned up on me the other day so once I get it fixed I'm going to leave the 60A bkr off. I was going to rewire the 150A ckt but the ac guy said my heat pump was putting out plenty of heat without it and that it would save money with one of the breakers tripped. But I was thinking it may just end up running longer and negate any savings.