:wall:grounding of main panels and subpanels

Hey guys, I just read something on another post and am confused. What is the correct method for grounding your panel itself to the ground or neutral bus? I've seen this both ways and I've always grounded to the grounding bus but both busses are connected anyway.
 
Sponsored Links
  #2  
Old 02-19-10, 10:14 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The ground and neutral bond depends on whether the panel is the service panel (first one after the meter that houses the main disconnect) or a subpanel; and also if is it located in the same building as the service panel. In any case however, the panel box itself is always connected solidly to the ground bus inside the panel.
 
  #3  
Old 02-19-10, 10:25 AM
Member
Thread Starter
Join Date: Dec 2009
Location: bond county illinois
Posts: 173
Received 0 Votes on 0 Posts
Thanx, IP. so what you're saying is the neutral and ground busses are connected in the service panel but not connected in the sub-panel?
 
  #4  
Old 02-19-10, 10:32 AM
palmcoast's Avatar
Member
Join Date: Dec 2006
Location: New Jersey
Posts: 105
Received 0 Votes on 0 Posts
On a sub panel you need to remove the jumper bar to isolate the nutrual bus from the ground bus. Both buses will then be mounted only on the unsulators without any contact to the panel therefore the ground bus will then have to be grounded to the panel. Most panel manufacturers will supply a seperate green screw that will be used to screw through the ground bus into the panel. If the subpanel is located in a seperate structure I believe a ground rod will be required.
 
  #5  
Old 02-19-10, 12:02 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Originally Posted by butcho View Post
Thanx, IP. so what you're saying is the neutral and ground busses are connected in the service panel but not connected in the sub-panel?
Yes that is correct. However, there are subpanels in outbuildings where ground and neutral are connected. It's not legal anymore as of 2008 code, but there are many grandfathered installations out there you might see in your travels.
 
  #6  
Old 02-19-10, 02:02 PM
Member
Thread Starter
Join Date: Dec 2009
Location: bond county illinois
Posts: 173
Received 0 Votes on 0 Posts
As always, Lots of good information.
Thanx again
 
  #7  
Old 02-19-10, 08:46 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,978
Received 21 Votes on 16 Posts
Originally Posted by ibpooks View Post
Yes that is correct. However, there are subpanels in outbuildings where ground and neutral are connected. It's not legal anymore as of 2008 code, but there are many grandfathered installations out there you might see in your travels.
It's also interesting to note that the 2008 code has not been universally accepted. Many areas are still under the 2005 or earlier codes.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: