I'm in the process of doing the rough in wiring for finishing our basement. There is one area that I would like to run about a 2 foot length of 14ga elec wire in a air return to the furnace. The air return is enclosed with wood and drywall on the bottom.

Is this allowed by code?

Thanks,

Harlan.
 
Sponsored Links
  #2  
Old 02-22-10, 08:52 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,978
Received 21 Votes on 16 Posts
Electrical wiring in a return air space must be in metal conduit, be a metallic sheathed cable, such as MC cable, or be rated for plenum use.
 
  #3  
Old 02-23-10, 05:29 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,909
Received 24 Votes on 20 Posts
Was this going to run parallel or perpendicular to the long dimension of the return?
 
  #4  
Old 02-23-10, 09:35 AM
Member
Thread Starter
Join Date: Jan 2002
Location: midwest
Posts: 296
Received 0 Votes on 0 Posts
long dimension, but only about 2 feet.
 
  #5  
Old 02-23-10, 09:48 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Unfortunately the code prohibits any romex from running in the long dimension of a cold air return regardless of length. It does allow runs in the perpendicular dimension, which would be 16" or 24" so perhaps your inspector may allow this if you mention it to him. An option to avoid the code issue would be to do this segment of wiring using metal clad (MC) cable and metal junction boxes which is allowed in the air handling space.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: