subpanel clearance

Knowing that breakers from a subpanel can't be more than 6'7" off ground and that there needs to be 36" clearance in front of the panel what about the sides of the panel? I've read 30" total in this forum and 30" to each side of the subpanel in other forums. If either side needs 30" clearance could an exterior door be located 30" or less from panel? The answer to this is very important as I have limited space and a workbench that may be affected. Any information would be appreciated.
 
Sponsored Links
  #2  
Old 03-27-10, 06:39 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,972
Received 59 Votes on 52 Posts
The 30" required can be anywhere in front of the panel. It can be measured from the left, right, or the panel can be in the middle. Just as long as there is 30" clear in front of the panel.
 
  #3  
Old 03-28-10, 05:58 AM
Member
Thread Starter
Join Date: Dec 2001
Location: United States
Posts: 46
Received 0 Votes on 0 Posts
Thanks that sounds much better. A book by Sunset stated a panel needed 30" on either side as well as 36" in front of the panel and that sounded pointless. In fact it would've really made the area useless to me negating the need for a subpanel.
 
  #4  
Old 03-28-10, 08:50 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,967
Received 2 Votes on 2 Posts
Think about most panels are on side walls in closets, and they are seldom more than 36"-48" deep to begin with, so having a 30" clearance on sides would be impractical.
 
  #5  
Old 03-28-10, 09:11 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,972
Received 59 Votes on 52 Posts
Originally Posted by idoltwilight View Post
Thanks that sounds much better. A book by Sunset stated a panel needed 30" on either side as well as 36" in front of the panel and that sounded pointless. In fact it would've really made the area useless to me negating the need for a subpanel.
Just to be clear you still need 36" deep of working space. Think of it as a box that is 30" wide and 36" deep in front of the panel.
 
  #6  
Old 03-28-10, 10:14 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
most panels are on side walls in closets,
But of course that is an electrical closet not a storage closet.
 
  #7  
Old 03-28-10, 01:49 PM
Member
Join Date: Feb 2006
Location: USA
Posts: 6,571
Received 4 Votes on 4 Posts
Clearance

If either side needs 30" clearance could an exterior door be located 30" or less from panel?
The door may be a part of the 30 in. space, as the space would not be affected when the door is closed. The work bench may not be in the space.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: