Amp load @ 240V vs 120V

Quick question for all of you, I know the question of whether a panel rated for [email protected] can supply [email protected] has been beaten to
death and is always a great argument starter. Here is a more realistic example,

If you have a subpanel fed by a 50amp dual pole breaker. Can this panel actually pull 100amps worth of 120V circuits.(Ignoring the 80% rule, balancing and such). This is due to each leg of the dual pole being able to supply 50 amps?

To simplify even more, could this panel have 5 fully loaded 20 amp circuits?
 
Sponsored Links
  #2  
Old 04-14-10, 10:53 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Originally Posted by rhiggins View Post
Can this panel actually pull 100amps worth of 120V circuits.(Ignoring the 80% rule, balancing and such).
Yes.

To simplify even more, could this panel have 5 fully loaded 20 amp circuits?
Yes.

In questions like these, it helps to convert to power (watts) so you are comparing the panels on level ground.

50A * 240V = 12,000W available at the panel

100A * 120V = 12,000W consumed by the circuits

Assuming perfect balance, and ideal breakers the power consumed is exactly equal to the power provided.
 
  #3  
Old 04-14-10, 10:55 AM
Member
Thread Starter
Join Date: Apr 2010
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
ibpooks, thanks for the clear answer, that is what I thought. Now to complicate things more, once you start loading a panel based on watts available, balancing becomes important, correct?
 
  #4  
Old 04-14-10, 10:58 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
If the load is close to the panel's limit, then yes balancing is a major issue. The panel also operates a bit more efficiently when balanced.

In your example, you could not have 60A on leg A and 40A on leg B because that imbalance would exceed the 50A feeder; however, 50A on leg A and leg B would be acceptable even though both configurations are 12kW.
 
  #5  
Old 04-14-10, 11:28 AM
Member
Thread Starter
Join Date: Apr 2010
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Thanks so much for your help!!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: