Lighting breaker trips ,then works fine
My lighting circut breaker keeps tripping. I replaced the breaker to rule that out. It runs lights only, no plugs. It will trip with all lights off. It will usually immediately trip when reset but after a minute will work fine for hours with all the lights on. There doesnt appear to be any pattern. Again, it will trip even if all the lights are off. Any suggestions on how to find the cause?
Have there been any recent changes to the circuit like new fixtures, dimmers or switches? Is it a standard breaker with a switch lever or an AFCI/GFCI breaker with a lever and "reset" button? What is the breaker brand?
no, no changes at all. The breaker is a standard breaker. The brand I used was Murray and thats what I took out. I did the entire wiring job 10 years ago as part of an addittion. Never had any issues. Just to point out, it is a seasonal home. I had the same thing happen a few months ago on a visit. Lights worked for a minute, then tripped and later worked the whole day after a few trips. When I came back yesterday. The breaker was tripped.(nothing was left on) Instantly tripped several times. After a few minutes they worked fine with all the lights on for several hours. Im baffled.
Seasonal home might be a clue. Any chance there's been some condensation build up inside light fixtures from the heating being turned off? What about rodents in the attic/basement/crawl where wiring runs?
No condensation that I see but I havent removed any fixtures at this point. Theres always a chance of rodents I guess but I havent noticed any in years. I keep it well ventilated so I dont believe moisture is an issue. Most of the lighting involved has insulation around it and a floor above it.
I had a service call similar to this problem
I end up opening all the fixture on that circuit,there was a wire shoring out in the fixture.
it took me some time to figure out.
Last edited by ibpooks; 04-14-10 at 01:25 PM. Reason: advertising links not allowed
I agree with Ibpooks, from the sound of things I think rodents chewing on your wire is a very likely cause. If you have a crawl space available to inspect the wiring, that's what I would check first.
thanks for the assistance. anyone have a good structured plan of attack? I can inspect only about 1/2 of the feed wire. The rest is buried in the ceiling. Finding no issues there, my plan is to inspect all the fixture connections and switch connections. Since it trips when the switches are off, I assume the fixtures are ok???? Then what ?
ok, went back today. After two days, breaker did not trip and all lights worked fine. Checked all fixtures and switch connections, all seemed fine.. no signs of any shorts or moisture. Checked about 1/2 of the feed line.. all was ok. Unable to check the rest since its buried in the ceiling/floor. No signs of any critters anywhere. I'm stuck at this point, especially since its so infrequent. Any ideas anyone? Can dimmers be a possibility? They are the toggle type that look just like a conventional switch. I have two of them installed but again, they work just fine. I'm baffled. If it kept tripping like it did twice before it would make the job easier!
If you can find some way to recreate the issue, you can sequentially remove items from the circuit and test that way. As you said that the fault occurs even when the switch is off, my guess is that it would have nothing to do with anything that the switch controls. Electrically, all that stuff shouldn't have any effect on the circuit with the switch off.
It could possibly be a dimmer switch with a short somewhere on the rheostat, where the short only happens if the rheostat is in a very specific position. You could try turning the circuit on and sliding the dimmer on to off slowly and see if you can pop the circuit that way. If so, new dimmer is needed.
Jim
When I did the install around 2000, all the feed goes to the light junction box and the power then goes from there to the switch and back to the light. All the fixtures are fine.. I turned them all on today and left them on.... The only patter Ive been able to see is it trips, and retrips several times , and within minutes will reset and work fine. Its been back on without triping since last tues. It was working fine two weeks ago after being vacant for 2 months. When I arrived this tuesday , it was tripped and again its been on since after several immediate trips and a change of the breaker(which didint help).