Hi Everyone,

I have seen all the rules about conduit sizing and the # of conductors allowed but I have not been able to locate
guidelines on when conduit is needed. I am rewiring my
house from scratch and will be installing a 100amp sub-panel.
The supply for the sub-panel will run through the attic. Do I
need to use conduit? Does it matter if it is EMT or plastic/PVC?

Thanks,

Victor
 
Sponsored Links
  #2  
Old 05-03-10, 12:34 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,982
Received 35 Votes on 30 Posts
Certain areas like Chicago require conduit. Other times it is only required as physical protection for a cable.

Can you describe how you will get from the panel to the new sub-panel? The cable would need protection if installed within 7' of the attic scuttle.
 
  #3  
Old 05-03-10, 12:35 PM
RHefferan's Avatar
Member
Join Date: Apr 2010
Location: Minnesota
Posts: 125
Received 0 Votes on 0 Posts
Originally Posted by VictorValencia View Post
Hi Everyone,

I have seen all the rules about conduit sizing and the # of conductors allowed but I have not been able to locate
guidelines on when conduit is needed. I am rewiring my
house from scratch and will be installing a 100amp sub-panel.
The supply for the sub-panel will run through the attic. Do I
need to use conduit? Does it matter if it is EMT or plastic/PVC?

Thanks,

Victor
You do not have to use conduit, you may use a service entrance cable of sufficient size. You may not run single wires without conduit.

If you use conduit, I would recommend EMT. PVC emits very toxic fumes when it burns. We all hope that never happens to your house, but it's safer to use EMT in that unfortunate possibility.
 
  #4  
Old 05-03-10, 01:51 PM
Member
Thread Starter
Join Date: May 2010
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
re: When is Conduit Needed?

Thanks for the feedback. I can make sure that the cable is more than 7' away from the attic scuttle. I will use a cable with all 3 wires. Am I supposed to use a 4th wire to ground the
2 panels together? Usually the metal conduit would provide
the connection.
 
  #5  
Old 05-03-10, 02:09 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
I will use a cable with all 3 wires. Am I supposed to use a 4th wire to ground the
2 panels together?
Cable should not be use in conduit except for short pieces of conduit for protection. You should use individual wires in a continuous conduit run. If cable is used the ground wire should be a part of the cable.
 
  #6  
Old 05-03-10, 02:29 PM
RHefferan's Avatar
Member
Join Date: Apr 2010
Location: Minnesota
Posts: 125
Received 0 Votes on 0 Posts
The big mistake that is most commonly made in sub panels is mixing of the ground and neutral because the panel bonding jumper is not removed. Many panels come with the main bonding jumper as a screw from the neutral bar to the case of the panel, bonding neutral and ground. For sub panels, this must be removed and neutral must stay completely isolated from ground. Only in the main panel should they be bonded.

As Ray said, the ground wire from the main to sub should be included in the cable, if you use cable. If you use metal conduit (no flex unless it's under 6'), that would be your ground path and a fourth wire would be unnecessary (unless it was a very short flex run, then you DO need the ground wire).

Rich
 
  #7  
Old 05-03-10, 04:21 PM
Member
Thread Starter
Join Date: May 2010
Location: USA
Posts: 16
Received 0 Votes on 0 Posts
re: When is Conduit Needed?

OK. I think I understand. The total run is approximately 50'. I will use a cable that has 4 wires and no conduit. I will make sure that the ground and neutral are not connected to each other in the sub-panel.

Thanks Everyone! I am sure this is not the last time you will hear from me......

Victor
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: