routing ground wire from indoor sub-panel

I'm running a feeder to a detached shop/office, via 3 underground conductors in conduit. They pass through two walls ( in 1 each 90 degree sweep around a corner ) to the sub-panel.

I need to ground the circuit(s), but I'm hesitant to pass a bare ground wire through the walls.

Am I to insulated it? Run it in metallic or non-metallic conduit? Or am I just worrying too much over nothing?
 
Sponsored Links
  #2  
Old 05-18-10, 01:07 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
The ground wire must run through the same conduit as the hot and neutral conductors. The conduit must be continuous box to box.

Metallic or non-metallic depends on the type of building, potential damage, burial depth, type of circuit, etc.
 
  #3  
Old 05-18-10, 01:18 PM
E
Member
Thread Starter
Join Date: Jan 2009
Location: Gulf Coast
Posts: 5
Received 0 Votes on 0 Posts
Ok ...

but NEC 2008 has a section for separate grounding systems for detached buildings: 250.32 .

What is not clear is what sort of protection the grounded conductor should or must have. If it were an outside panel I'd just run it bare to the first rod.

I found where you had posted this :http://forum.doityourself.com/electr...ml#post1563327
earlier. Does this address my question?
 
  #4  
Old 05-18-10, 01:31 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
Okay that makes some more sense. You're talking about the grounding electrode conductor; the "grounding conductor" and "grounded conductor" are different.

If the GEC is #8, it should run through wall spaces, bored holes and stapled similar to romex installation. It should be sleeved in PVC conduit where exposed outdoors for protection. Don't use metal conduit in this case.

If the GEC is #6 or larger it can run unprotected through the wall cavity and outdoors to the ground rod simply stapled to the building exterior or similarly fastened.
 
  #5  
Old 05-18-10, 01:52 PM
E
Member
Thread Starter
Join Date: Jan 2009
Location: Gulf Coast
Posts: 5
Received 0 Votes on 0 Posts
Thank you!

Grounding Electrode Conductor - exactly so.
 
  #6  
Old 05-18-10, 02:20 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
I'm running a feeder to a detached shop/office, via 3 underground conductors in condui
If the conduit is PVC you must also have a ground wire.
 
  #7  
Old 05-18-10, 03:39 PM
E
Member
Thread Starter
Join Date: Jan 2009
Location: Gulf Coast
Posts: 5
Received 0 Votes on 0 Posts
A grounding conductor in the conduit?

This puts me up to 4 conductors. Does this mean I have to derate the conductors to 80%?

I was running 3 each #2 copper for a 100A service in 2" schedule 80 PVC.
 
  #8  
Old 05-18-10, 03:49 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,258
Received 102 Votes on 95 Posts
Originally Posted by Ecclesiastes View Post
This puts me up to 4 conductors. Does this mean I have to derate the conductors to 80%?
Nope, you have to derate after 9 current carrying conductors. In your case, you only have two (the two hots). In theory, the neutral is not current carrying since a perfectly balanced load will provide 0A on the neutral conductor. Though this will never happen in real life, you still don't have to consider it a current carrying conductor.
 
  #9  
Old 05-18-10, 05:18 PM
E
Member
Join Date: Feb 2010
Location: United States
Posts: 461
Received 0 Votes on 0 Posts
Originally Posted by Zorfdt View Post
Nope, you have to derate after 9 current carrying conductors. In your case, you only have two (the two hots). In theory, the neutral is not current carrying since a perfectly balanced load will provide 0A on the neutral conductor. Though this will never happen in real life, you still don't have to consider it a current carrying conductor.
Not sure where you get your information. Neutrals are always counted as current carrying conductors for derating purposes. When talking about having 9 CCC's in a pipe, neutrals are always counted.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: