holes/cables in studs, 1-1/4 or 1-1/2 inches??

“The holes and the cable running through them must be at least 1-1/4 in. from both faces of the stud to prevent nails and screws from hitting the cable”

I think I found the above quote on this message board somewhere, but my question is – is the requirement 1-1/4 inches or 1-1/2 inches? I’m in Bergen county NJ. I read something about 1-1/2 inches this morning, after I’d drilled all of my holes at least 1-/1/4 inches back from the faces of the studs. New I’m worried the inspector may make me add nail plates.

Thanks, Mike
 
  #2  
Old 06-24-10, 08:40 AM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 21,112
Received 4 Votes on 4 Posts
Well, Mike...no Pro.. but if you think about it...if it were 1 1/2", you could only have a 1/2" hole in a standard 2x4 stud. With 1 1/4" you could have up to a 1" hole...

I think 1 1/4" is the right number.


Yep...found this....

FLOOR JOISTS/RAFTERS

Holes: Do not bore holes closer than 2" from joist edges, nor make them larger than 1/3 the depth of the joist.
Notches: Do not make notches inthe middle third of the span where the bending forces are greatest.
Notches should be no deeper than 1/6 the depth of the joist. Notches at the end of the joist should be no deeper than 1/4 the depth. Limit the length of notches to 1/3 of the joist’s depth.

WALL STUDS

1” is the max diameter , we can have in 2 x 4 [3.5”] studs and avoid the 1/16” nailer plates due to the 1.25” NEC rule. (NEC rule: all wires must maintain a minimum of 1.25" from edge of stud on both sides) If you end up getting closer than this then install a metal nail plate across the studs edge. Three NM-B 12-2G ,Romex® will not require a hole larger than 1"..as 3/4" is a bit traumatic on the sheath, when pulling (3)size 12-2G NM cable.

¾” hole for (3) 14-2G

1” hole for (3) 12-2G

For structural (not electrical) reasons, keep your bored holes dead center top to bottom, and at least three inches apart (edge to edge). Don't drill through any trusses whats so ever.

Never drill any holes in TRUSS members..
 
  #3  
Old 06-24-10, 09:07 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,942
Received 44 Votes on 42 Posts
The requirement is 1-1/4" from the nailing face of the framing member. If you have any that are shallower all you need to do is install a steel nailing plate on the stud(s) where the cable is shallow. I usually drill 7/8" auger holes through the center of the 2x4 stud.
 
  #4  
Old 06-24-10, 03:52 PM
E
Member
Join Date: Feb 2010
Location: United States
Posts: 461
Received 0 Votes on 0 Posts
I agree, im in jersey as well and i always just use 7/8" auger bits. Its easier to just buy and use one size of bit for all my holes. I never bundle more than 3 wires, and (3) 12/2's fit nicely in a 7/8" hole. in the rare instance i run bigger wire than 6/3, i just use spade bits or forstner bits. Sometimes i drop to a 1/2 or 3/4" bit for low voltage wiring, unless im running quite a few then i stick with the 7/8"
 
 