Corrosion inhibitor necessary?

Seems to me I was told that it is necessary to apply a substance called "Noalax" (sp?) whenever you were to have aluminum to copper contact. Is that still the case? Is it dangerous to pigtail copper onto aluminum without any inhibitor in a 15- or 20-amp outlet?
 
  #2  
Old 07-27-10, 02:39 PM
HotxxxxxxxOKC's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2006
Location: USA
Posts: 8,034
Received 0 Votes on 0 Posts
Only if the manufacture requires it. Also, ensure each part is rated for Al and Cu.
 
  #3  
Old 07-27-10, 06:12 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,794
Received 100 Votes on 90 Posts
Originally Posted by sailor86 View Post
Seems to me I was told that it is necessary to apply a substance called "Noalax" (sp?) whenever you were to have aluminum to copper contact. Is that still the case? Is it dangerous to pigtail copper onto aluminum without any inhibitor in a 15- or 20-amp outlet?
I can't think of a single situation where aluminum and copper wire should be or would be allowed to be in direct contact unless it is with a listed connector such as the Ideal purple Twister connectors that are UL listed for connecting aluminum to copper wire.
 
  #4  
Old 07-27-10, 06:59 PM
5
Member
Join Date: Nov 2004
Location: CA
Posts: 2,039
Received 0 Votes on 0 Posts
It is called " NoAlOx" which stands for NO ALUMINUM OXIDATION, but using that does not for example allow you to connect aluminum to a device which says "copper only"
 
  #5  
Old 07-27-10, 08:02 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,952
Received 303 Votes on 262 Posts
Originally Posted by CasualJoe View Post
I can't think of a single situation where aluminum and copper wire should be or would be allowed to be in direct contact unless it is with a listed connector such as the Ideal purple Twister connectors that are UL listed for connecting aluminum to copper wire.
One of the most common places where you have this type of connection is in electrical panels. Almost all of the neutral/ground lugs and the lugs on the main breaker/main lugs are aluminum and you connect copper wire to them. No paste required if using copper. These are also listed CU/AL.
 
  #6  
Old 07-27-10, 09:49 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,794
Received 100 Votes on 90 Posts
But.....aluminum lugs and neutral bars marker CU/AL are tin plated. If this were not the case, copper and brass lugs would accept aluminum wire, but they are marked CU only unless they are tin plated.
 
  #7  
Old 07-28-10, 09:53 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,942
Received 44 Votes on 42 Posts
I always put no-ox grease on aluminum connections, however you should never have a direct aluminum to copper splice without an approved connector in between.
 
 