Running wires to garage.
Old 10-04-10, 05:11 PM
bobbi 5's Avatar
I want to run two circuits to my garage useing one 12-3 romex can i use a 20 amp tandem breaker with a bridge clip betwwen the handles. they have holes in the handles
Old 10-04-10, 05:40 PM
CasualJoe's Avatar
Received 188 Upvotes on 168 Posts
Short answer is NO. A typical 20 amp tandem is two single pole breakers that each draw their power from the same bus stab (same line). In order to use a common neutral (multi wire branch circuit) you must draw power on the two circuits from separate lines entering the panel, other wise you would overload the neutral. To run a common neutral in a multi wire branch circuit you must use a 2 pole breaker, not a tandem.
Old 10-04-10, 05:44 PM
ray2047's Avatar
Only if you are referring to a half size 240v 2 pole breaker. Note if this is a GE box you must be very careful that it goes on both hots. You can not use a tandem intended as two single pole breakers on the same hot.
Old 10-04-10, 05:59 PM
bobbi 5's Avatar
so to use a 20 amp tandem i have to run 2, 12-2 romex wires
Old 10-04-10, 06:27 PM
CasualJoe's Avatar
That's correct. That way each circuit has it's own dedicated neutral conductor.
Old 10-04-10, 07:53 PM
pcboss's Avatar
Received 201 Upvotes on 176 Posts
Your feeder to the outbuilding is limited to one circuit. You cannot run 2 12-2s to the building. You can run one multi-wire branch circuit on a 12-3.
Old 10-05-10, 05:39 PM
CasualJoe's Avatar
I don't think the OP stated whether this was an attached garage or a detached garage. Perhaps this is a good time to ask that question. If it is detached, pcboss is correct, you cannot run two separate 12-2s to a detached outbuilding.
Old 10-05-10, 09:50 PM
bobbi 5's Avatar
its an attached garage i just wanted to add some more circuits
Old 10-05-10, 11:06 PM
F
Received 39 Upvotes on 31 Posts
There is no problem in running as many circuits as you desire to an attached garage.