GFCI in garage


  #1  
Old 10-10-10, 07:51 AM
E
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
GFCI in garage

Hello again everyone,

I have a 20a circuit coming from the panel to a new wall, the way the path worked out, (the current plan is) it will got to a 4x4x 2 1/8 junction box with a mud ring for a single gfci rec. inside the box will be 3 12ga. loads pigtailed together (they branch off in different directions to 3 other single receptacles in the shop) and drawn off the load side of the gfci. the box looks busy to me and I think it would be roomier if I add a extension ring. anything wrong with a gfci rec in a sestup like this?

thanx for your help Eric
 
  #2  
Old 10-10-10, 08:10 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,389
Received 148 Votes on 131 Posts
Your box is listed for 13 conductors, plus the volume of the mud ring. The volume is listed at 30.3 cubic inches.

4 12-2 cables = 8
1 ground = 1
device = 2
total 11 #12s at 2.25 each = 24.75

Your box is big enough.
 
 