only about 70 vac at light switch and rec.??? help

At the light switch I can measure from ground wire to hot (black) and get 120v. However if I measure from neutral (white) to hot (black) I only get about 70v. There is a receptical on the circuit that does the same. I have not traced the wire from receptical yet.

I am thinking open neutral somewhere. Does this sound correct or am I off base? Any help is greatly appreciated. thanks.
 
Sponsored Links
  #2  
Old 10-24-10, 04:30 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,663
Received 87 Votes on 77 Posts
Not an open neutral, but a poor and/or loose neutral connection. Seen it many times.
 
  #3  
Old 10-24-10, 05:23 PM
K
Member
Thread Starter
Join Date: Jun 2005
Location: USA
Posts: 654
Received 0 Votes on 0 Posts
with your experience, any suggestions on fastest way to trace it down? thanks
 
  #4  
Old 10-24-10, 10:14 PM
S
Member
Join Date: Dec 2006
Location: orange county
Posts: 285
Received 0 Votes on 0 Posts
I would check the receptacles on that circuit for poor back-stab connections.
 
  #5  
Old 10-24-10, 10:37 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
You also need to redo all wire nut connections on the circuit including at switches and lights.
 
  #6  
Old 10-24-10, 11:03 PM
F
Member
Join Date: Mar 2006
Location: NE Wis / Paris France{ In France for now }
Posts: 4,807
Received 0 Votes on 0 Posts
Backstabbed devices and bad connecton like poor wirenut connection is the most common curpit and the way you tell us the voltage that mean bad conenction on netural conductor so check that circuit for any issue with connection and if bad badstabbed move them to screw and toqure them down good.

And when you check the netural connections with wirenuts it will be wise to buy new wirenuts as well they are pretty cheap and it will really slove the issues.

If you have alum conductors stop right there and let us know ASAP we will tell you the correct way to deal with it.

Merci.
Marc
 
  #7  
Old 10-25-10, 04:36 AM
K
Member
Thread Starter
Join Date: Jun 2005
Location: USA
Posts: 654
Received 0 Votes on 0 Posts
Thanks for the help. I will try to fix it today. Update later.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: