Why are incandescent blubs blowing out?
This a single family house with new (2 year old 100amp service). For some time new bulbs in many places in the house continue to blow out after just a short time in use. The condition seems to be getting worse. I assume this could be hazardous.? What could be the cause? I think I need an electrician?
#3
Actually anything up to 127v is probably ok. You need to check all your connections to be sure they are tight. Turn off the main breaker and check all the neutrals in the main box are tight. Be very careful even with the main breaker off there are exposed live areas around the main breaker. You can try tightning the main neutral but don't go near the main breaker.
#4
Member
Join Date: Dec 2010
Location: usa
Posts: 206
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You may have high voltage due to your location, say maybe close to a large sub station etc. and you might have to switch to name brand 130 volt bulbs. That is common where I live. Of course the incandescent lamp is going out of existance down the road so you might want to switch for CFL's and give those a try (compact flourescents). Apart from the cost the only real problem there is that most won't work on dimmers. There are CFL's that are dimmable but you need to be careful to get correct dimmer...
#6
Member
Thread Starter
Join Date: Feb 2009
Location: New Jersey
Posts: 101
Upvotes: 0
Received 0 Upvotes
on
0 Posts
UPDATE:
Measured voltage at about 127.8. Called the power company and they sent a tech to have a look. He noticed that the electricians had a questionable ground where the line enters the conduit on the side of the house. He said he sees this often and this can cause problems. He went up on the side of the house and redid the ground. They are sending someone else with an instrument that will look for voltage spikes. I will see what happens.
Measured voltage at about 127.8. Called the power company and they sent a tech to have a look. He noticed that the electricians had a questionable ground where the line enters the conduit on the side of the house. He said he sees this often and this can cause problems. He went up on the side of the house and redid the ground. They are sending someone else with an instrument that will look for voltage spikes. I will see what happens.
#9
That is little high for that voltage level when they did mesaure that voltage during the moring or afternoon due some case they may have a power factor correcting device on the POCO line which it can affected it..
Many POCO will have to follow the NSEC regulations about voltage varations they will alllowed +- 10% the most { unless written in the state or local regulation }
The other casue may read little high if you are not very far from substation which it will happend as well.
Let the POCO take a recording on voltage level for at least 24 hours to make sure and they will have to adjust the transfomer tap or get diffrent transfomer to compreasied the voltage differnice.
Merci.
Marc
Many POCO will have to follow the NSEC regulations about voltage varations they will alllowed +- 10% the most { unless written in the state or local regulation }
The other casue may read little high if you are not very far from substation which it will happend as well.
Let the POCO take a recording on voltage level for at least 24 hours to make sure and they will have to adjust the transfomer tap or get diffrent transfomer to compreasied the voltage differnice.
Merci.
Marc