Wires in conduit
#1
Wires in conduit
I am helping a friend who is starting back up on an existing project. He has 8 pairs of white and black wires run through about 20' of conduit. What is the easiest way to match up the white and blacks for each circuit? He didn't mark any of them.
#3
Rays way is the most foolproof. Sometimes you can also tug on one end while someone watches the other end of the conduit.
Did your friend consider ther derating issues before installing that many conductors in the conduit?
Did your friend consider ther derating issues before installing that many conductors in the conduit?
#5
If the white wires are all neutrals, it doesn't matter much which white wire you pair with a black wire as they all terminate in the neutral bus anyway. For only 20 feet of conduit, I like the tug method pcboss mentioned.
#9
Yes, they are. I can't recall the code reference but I believe 2008 cod requires circuits in the same pipe to be grouped together. (IE: hot with it's neutral or hots together.)
Your good then.
My miistake, it is actually a total of 4 white, 4 black and 1 ground in a 3/4" conduit.
#10
I am not trying to argue, but looking for clarification. Now we are at 4 white conductors, 4 black conductors and 1 green grounding conductor in a single 3/4" conduit. At the panel, each white terminates on the neutral bar, each black terminates at a single pole breaker and the grounding conductor terminate at the ground bar (my assumption). Assuming the other end is a junction box and all conductors are the same size, what difference does it make which white conductor is paired with a specific black conductor? OR....is the code reference requiring that each pair at each end by ty wrapped together to form a group? I have a 2008 Analysis of Changes book, I'll see if I can find anything on this.
#11
Member
Black and White Pairs
Would matching pairs be necessary when using arc fault breakers? I am thinking yes. What do the pros think?
#12
I'd say yes to that question too because each neutral conductor has to terminate on the same breaker as the hot conductor it is the match too. But what we were discussing is different, all the neutral conductors go to the neutral bar.
#13
Member
Join Date: Apr 2009
Location: Boston
Posts: 124
Upvotes: 0
Received 0 Upvotes
on
0 Posts
(A) Conductors Grouped Together. Where conductors
carrying alternating current are installed in ferrous metal
enclosures or ferrous metal raceways, they shall be arranged
so as to avoid heating the surrounding ferrous metal
by induction. To accomplish this, all phase conductors and,
where used, the grounded conductor and all equipment
grounding conductors shall be grouped together.
Exception No. 1: Equipment grounding conductors for
certain existing installations shall be permitted to be installed
separate from their associated circuit conductors
where run in accordance with the provisions of 250.130(C).
Exception No. 2: A single conductor shall be permitted to
be installed in a ferromagnetic enclosure and used for skineffect
heating in accordance with the provisions of 426.42
and 427.47.
#14
300.20
(A) Conductors Grouped Together. Where conductors
carrying alternating current are installed in ferrous metal
enclosures or ferrous metal raceways, they shall be arranged
so as to avoid heating the surrounding ferrous metal
by induction. To accomplish this, all phase conductors and,
where used, the grounded conductor and all equipment
grounding conductors shall be grouped together.
Exception No. 1: Equipment grounding conductors for
certain existing installations shall be permitted to be installed
separate from their associated circuit conductors
where run in accordance with the provisions of 250.130(C).
Exception No. 2: A single conductor shall be permitted to
be installed in a ferromagnetic enclosure and used for skineffect
heating in accordance with the provisions of 426.42
and 427.47.
(A) Conductors Grouped Together. Where conductors
carrying alternating current are installed in ferrous metal
enclosures or ferrous metal raceways, they shall be arranged
so as to avoid heating the surrounding ferrous metal
by induction. To accomplish this, all phase conductors and,
where used, the grounded conductor and all equipment
grounding conductors shall be grouped together.
Exception No. 1: Equipment grounding conductors for
certain existing installations shall be permitted to be installed
separate from their associated circuit conductors
where run in accordance with the provisions of 250.130(C).
Exception No. 2: A single conductor shall be permitted to
be installed in a ferromagnetic enclosure and used for skineffect
heating in accordance with the provisions of 426.42
and 427.47.
#15
Member
Join Date: Apr 2009
Location: Boston
Posts: 124
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If you wanted to you can pair the branch by fastening the ungrounded to the grounded conductor prior to pulling the wire by a means which would not damage the conductors (tape)
I believe their intent is to make sure the return path is in the same conduit to cancel inductive heating, I believe this to comply with grouping.
I believe their intent is to make sure the return path is in the same conduit to cancel inductive heating, I believe this to comply with grouping.
#16
300.20
(A) Conductors Grouped Together. Where conductors
carrying alternating current are installed in ferrous metal
enclosures or ferrous metal raceways, they shall be arranged
so as to avoid heating the surrounding ferrous metal
by induction. To accomplish this, all phase conductors and,
where used, the grounded conductor and all equipment
grounding conductors shall be grouped together.
Exception No. 1: Equipment grounding conductors for
certain existing installations shall be permitted to be installed
separate from their associated circuit conductors
where run in accordance with the provisions of 250.130(C).
Exception No. 2: A single conductor shall be permitted to
be installed in a ferromagnetic enclosure and used for skineffect
heating in accordance with the provisions of 426.42
and 427.47.
(A) Conductors Grouped Together. Where conductors
carrying alternating current are installed in ferrous metal
enclosures or ferrous metal raceways, they shall be arranged
so as to avoid heating the surrounding ferrous metal
by induction. To accomplish this, all phase conductors and,
where used, the grounded conductor and all equipment
grounding conductors shall be grouped together.
Exception No. 1: Equipment grounding conductors for
certain existing installations shall be permitted to be installed
separate from their associated circuit conductors
where run in accordance with the provisions of 250.130(C).
Exception No. 2: A single conductor shall be permitted to
be installed in a ferromagnetic enclosure and used for skineffect
heating in accordance with the provisions of 426.42
and 427.47.
#17
If you wanted to you can pair the branch by fastening the ungrounded to the grounded conductor prior to pulling the wire by a means which would not damage the conductors (tape)
I believe their intent is to make sure the return path is in the same conduit to cancel inductive heating, I believe this to comply with grouping.
I believe their intent is to make sure the return path is in the same conduit to cancel inductive heating, I believe this to comply with grouping.
#18
Member
Neutrals
all the neutral conductors go to the neutral bar.
#19
I paired them and checked the continuity to match them up. Two circuits were for bedroom ARC fault breakers and two were lighting circuits. Thank you very much for the help.
#20
True, it was an assumption because of no mention of either a GFCI or AFCI in the OP. Where would you have assumed them to go, given the information provided? Now, from the latest post we see that two circuits were indeed AFCI circuits and that two of the white conductors would have to be paired with black conductors.