Add a switch next to an outlet?
Old 01-16-11, 03:34 PM
I have a small bank of cabinets on a wall in my kitchen. There is a single gang electrical box with a GFCI on this wall and I want to hard wire switched under-cabinet lighting in this location.
My plan is to remove the single gang box, replace it with a two gang box and add a switch next to the GFCI. I wish to pull power from the GFCI for the switch.
I'm believe there are two 14/2 cables in this box (power coming in going out).
Not sure how to get power from the GFCI to the switch. Any simple diagrams I can reference?
TIA.
Tipsy
Old 01-16-11, 03:55 PM
ray2047's Avatar
Countertop kitchen receptacle circuits by code can not be used for lighting.
That would not be code compliant for a countertop receptacle. It should be #12 on a 20a breaker.
pcboss's Avatar
The small appliance countertop circuits cannot be used to power hard-wired lighting. You will need to find another source of power.
The correct size wire for the 20 amp receptacle circuits would be #12.
Old 01-16-11, 04:02 PM
It's probably 12#...it's original to the house. I was assuming it was 14# but I'm probably wrong.
Tipsy
Old 01-16-11, 04:05 PM
Or just eliminate the outlet and replace it with a switch?
Tipsy
Old 01-16-11, 04:10 PM
ray2047's Avatar
No, it would still be on a prohibited branch circuit plus the receptacle spacing would probably no longer be code compliant.
Old 01-16-11, 04:16 PM
Too bad.
Thanks for the info.
Tipsy
Old 01-16-11, 04:59 PM
pcboss's Avatar
Tipsy
The receptacle is probably needed to meet the receptacle spacing requirements in addition
to the prohibition against being used for the lighting.
Old 01-17-11, 07:53 AM
Justin Smith's Avatar
What sections are the kitchen counter requirements?
Old 01-17-11, 09:03 AM
ray2047's Avatar
210.52 is one section. For instance relevant to this post is 210.52.b
(2) no other outlets. The two or more small-appliance
branch circuits specified in 210.52(b)(1) shall have no
other outlets.