Add a switch next to an outlet?
I have a small bank of cabinets on a wall in my kitchen. There is a single gang electrical box with a GFCI on this wall and I want to hard wire switched under-cabinet lighting in this location.
My plan is to remove the single gang box, replace it with a two gang box and add a switch next to the GFCI. I wish to pull power from the GFCI for the switch.
I'm believe there are two 14/2 cables in this box (power coming in going out).
Not sure how to get power from the GFCI to the switch. Any simple diagrams I can reference?
TIA.
Tipsy
My plan is to remove the single gang box, replace it with a two gang box and add a switch next to the GFCI. I wish to pull power from the GFCI for the switch.
I'm believe there are two 14/2 cables in this box (power coming in going out).
Not sure how to get power from the GFCI to the switch. Any simple diagrams I can reference?
TIA.
Tipsy
#2
I wish to pull power from the GFCI for the switch.
I'm believe there are two 14/2 cables in this box
#3
The small appliance countertop circuits cannot be used to power hard-wired lighting. You will need to find another source of power.
The correct size wire for the 20 amp receptacle circuits would be #12.
The correct size wire for the 20 amp receptacle circuits would be #12.
#4
Member
Thread Starter
Join Date: Apr 2004
Location: FL & NYC
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Tipsy
#5
Member
Thread Starter
Join Date: Apr 2004
Location: FL & NYC
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Tipsy
#6
No, it would still be on a prohibited branch circuit plus the receptacle spacing would probably no longer be code compliant.
#7
Member
Thread Starter
Join Date: Apr 2004
Location: FL & NYC
Posts: 16
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the info.
Tipsy
#8
to the prohibition against being used for the lighting.
#10
What sections are the kitchen counter requirements?
(2) no other outlets. The two or more small-appliance
branch circuits specified in 210.52(b)(1) shall have no
other outlets.
branch circuits specified in 210.52(b)(1) shall have no
other outlets.