connect double wall oven electric wire question


  #1  
Old 01-19-11, 05:51 AM
V
Member
Thread Starter
Join Date: Jan 2011
Location: usa
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
connect double wall oven electric wire question

Hi,

I am replacing a double wall oven and would like some clarity on the wiring. I have an existing 50 amp 240V 3 wires coming from the junction box. it has a black, black with Red stripes (no that visible), and Bare wire. My Kenmore oven has a black, red, white, and bare wire. Base on the instruction from my new oven, the white and bare wire from the oven connect to the bare wire. what is the black wire from the oven connect to? black to -> black with red stripes or black?

Thanks
 
  #2  
Old 01-19-11, 08:23 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
It would be best to run new wiring. You have a 240v service at the wall. You need a 120/240v service. It has not been code compliant to use a bare wire for neutral for many decades. If this is conduit you can probably pull a new wire for the neutral. If this is cable you should run new cable.
 
  #3  
Old 01-19-11, 08:27 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
The black and red are interchangeable. It doesn't matter which goes to which. This is no problem as long as the existing wires are copper. If they are aluminum, please let us know as this complicates the installation.

To continue with what Ray said, your existing circuit is grandfathered so it is legal to continue using it, but it is not up to modern standard.
 
  #4  
Old 01-19-11, 08:34 PM
V
Member
Thread Starter
Join Date: Jan 2011
Location: usa
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks

Ray and Ben, The existing wires both black and black with red stripes are copper wire. Thank you both for your response.

Vinh
 
 